Proper Seperation between direct buried communications and power cable

Status
Not open for further replies.

sdiess

New member
I have to place a 200 pair copper phone line between 2 buildings. I will be running parallel with the main power service for a building. The 200 pair will be a direct buried cable and the power feed is in conduit. What is the NEC code for separation between the two cables? I know BICSI says 24".

Thanks
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I think the NEC would be perfectly happy if you ran the cable right alongside the conduit. Might not be ideal for whatever data is on that cable, but that is a design issue.
 

Davis9

Senior Member
Location
MA,NH
Here the local utilities say 12", but when you get to the pole it's everyman for themselves most times.

Tom
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
If this is metallic conduit, I wouldn't sweat it at all. If PVC, a foot should be plenty. Twisted-pair is suprisingly immune to interference.
 