Low voltage and other systems

Status
Not open for further replies.

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: Low voltage and other systems

The rule in 300.8 says no, but if the low voltage wiring is an Article 725 installation, than 300.8 does not apply because 725.3 says that only the sections of Article 300 that are referenced in Article 725 shall apply. 300.8 is not referenced in 725.
Don
 

tom baker

First Chief Moderator
Staff member
Re: Low voltage and other systems

This issue has come up several times on the forum. As Don says 725.3 may allow it. Perhaps there is a proposal for the 2005 NEC that someone could comment on regarding this issue just to see what the CMP allows.
 