What does it take to change a class A style 6 system to a class A style 7?
Unfortunately, the code does not indicates how often the modules are needed, just that it needs to perform during a wire to wire fault. If you only put the modules every 25 devices, then during a fault the 25 devices in between the modules will not function.
you need one at panel for begining of loop then one at 25 devices and one more at panel for return of the loop. ALSO you need one if you go between floors
yes peter d you are correct sorry for giving bad info.