    Arch Fault protection in Dormitories

    Is arch fault protection required in dormitory rooms without cooking facilities?

    #2
    See 210.18. Now, if the AHJ considers dorm rooms something other than Guest rooms or Suites you may have another situation. NC makes up their own rules for dorm rooms under State Construction jurisdiction

    Roger
    Last edited by roger; 12-05-12, 09:04 AM.
    Moderator

    Comment


      #3
      ark fault in dorm

      does anyone have info how nyc considers a dorm

      Comment


        #4
        Originally posted by contactm View Post
        does anyone have info how nyc considers a dorm
        Sure, do you have a specific question?
        Rob

        Moderator

        All responses based on the 2017 NEC unless otherwise noted

        Comment


          #5
          I usually don't care, but, in 2 0f the first 3 posts we had "arch" fault and "ark" fault questions. This is an electrical forum. We deal in "arc" faults
          Mike, Dutchess County, NY

          Comment


            #6
            is a arc fault breaker needed for a dorm room in new york city

            Comment


              #7
              Originally posted by contactm View Post
              is a arc fault breaker needed for a dorm room in new york city
              Which code cycle are you under? For the 2006 NYC Electrical Code based on the 2005 NEC and the NYC 2011 Electrical Code Administrative Provisions based on the 2008 NEC have slightly different requirements.

              In answer to your question the answer is yes under either of the code cycles mentioned above. The 2006 has a slightly different requirement for other portions of dormitories.
              Rob

              Moderator

              All responses based on the 2017 NEC unless otherwise noted