I am looking for where it would say in the code book where you could not use the neutral as a
ground. I know it is not good practice, have a builder wanting me to show him where it is against code. :?
250.142 Use of Grounded Circuit Conductor for Grounding Equipment.
(A) Supply-Side Equipment. A grounded circuit conductor shall be permitted to ground non–current-carrying metal parts of equipment, raceways, and other enclosures at any of the following locations:
(1) On the supply side or within the enclosure of the ac service-disconnecting means
(2) On the supply side or within the enclosure of the main disconnecting means for separate buildings as provided in
250.32(B)
(3) On the supply side or within the enclosure of the main disconnecting means or overcurrent devices of a separately derived system where permitted by
250.30(A)(1)
On the supply side of a separately derived system disconnecting means, the grounded circuit conductor is permitted by
250.142(A) to ground non–current-carrying metal parts of equipment, raceways, and other enclosures, which is similar to the grounding and bonding of the same types of equipment on the line side ofa service-supplied system.
(B) Load-Side Equipment. Except as permitted in
250.30(A)(1) and
250.32(B) Exception, a grounded circuit conductor shall not be used for grounding non–current-carrying metal parts of equipment on the load side of the service disconnecting means or on the load side of a separately derived system disconnectingmeans or the overcurrent devices for a separately derived system not having a main disconnecting means.
Exception No. 1: The frames of ranges, wall-mounted ovens, counter-mounted cooking units, and clothes dryers under the conditions permitted for existing installations by
250.140 shall be permitted to be connected to the grounded circuit conductor.
Exception No. 2: It shall be permissible to ground meter enclosures by connection to the grounded circuit conductor on the load side of the service disconnect where all of the following conditions apply:
(1)
No service ground-fault protection is installed.
(2)
All meter enclosures are located immediately adjacent to the service disconnecting means.
(3)
The size of the grounded circuit conductor is not smaller than the size specified in
Table 250.122 for equipment grounding conductors.
Exception No. 3: Direct-current systems shall be permitted to be grounded on the load side of the disconnecting means or overcurrent device in accordance with
250.164.
Exception No. 4: Electrode-type boilers operating at over 600 volts shall be grounded as required in
490.72(E)(1) and
490.74.