Hendrix
- New England
Can this be a "substitute" for gnd. rods?
"can be" or "is"If you have a building with a concrete encased electrode that can be all that is required. Of course if it has a metal water service you would have to use that as well.
"can be" or "is"
Can be unless others are available, then they must be tied together
250.50 Grounding Electrode System.
All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system. Where none of these grounding electrodes exist, one or more of the grounding electrodes specified in 250.52(A)(4) through(A)(8) shall be installed and used.
Note only section titles was quoted here250.52 Grounding Electrodes.
(A) Electrodes Permitted for Grounding.
(1) Metal Underground Water Pipe.
(2) Metal Frame of the Building or Structure.
(3) Concrete-Encased Electrode. A concrete-encased electrode shall consist of at least 6.0 m (20 ft) of either (1) or (2):
(4) Ground Ring.
(5) Rod and Pipe Electrodes.
(6) Other Listed Electrodes.
(7) Plate Electrodes.
(8) Other Local Metal Underground Systems or Structures.
if there are multiple,
approved type of grounding electrodes present at a site,
then they must all be bonded together [ RE: Article 250.50,
'08 NEC ].
So if you have a ground rod on the truck, does that mean it's "present" and you have to use it
Since "present" isn't specifically defined, an AHJ could possibly interpert it that way.
Steve
"Present" as present in the installed system. I do not believe or could possibly conceive that an AHJ would even consider your thought pattern.
But some idiot somewhere will think an abandoned ground rod still in the dirt from a previous installation needs to be connected because it is "present"
What if it's a 10' rod :lol:Dig down 2" and cut an inch off. Now it's no longer an electrode. :roll:
Cover up the end with dirt.What if it's a 10' rod :lol: