Concrete encased electrode

Status
Not open for further replies.

north star

Senior Member
Location
inside Area 51
= $ =

Hendrix,

In agreement with the other esteemed Forum contributors,
"yes" CEE's can be a substitute for grnd. rods, and as
**Gregg Harris** stated, ...if there are multiple,
approved type of grounding electrodes present at a site,
then they must all be bonded together [ RE: Article 250.50,
'08 NEC ].

= $ =
 

kwired

Electron manager
Location
NE Nebraska
From 250 part III:

250.50 Grounding Electrode System.

All grounding electrodes as described in 250.52(A)(1) through (A)(7) that are present at each building or structure served shall be bonded together to form the grounding electrode system. Where none of these grounding electrodes exist, one or more of the grounding electrodes specified in 250.52(A)(4) through(A)(8) shall be installed and used.


250.52 Grounding Electrodes.

(A) Electrodes Permitted for Grounding.

(1) Metal Underground Water Pipe.

(2) Metal Frame of the Building or Structure.
(3) Concrete-Encased Electrode. A concrete-encased electrode shall consist of at least 6.0 m (20 ft) of either (1) or (2):
(4) Ground Ring.
(5) Rod and Pipe Electrodes.
(6) Other Listed Electrodes.
(7) Plate Electrodes.
(8) Other Local Metal Underground Systems or Structures.
Note only section titles was quoted here

If items 1 through 7 are present you must use them. Items 4 through 7 are typically only present if one intentionally places them to use an an electrode. Items 1 through 3 are either there or they are not as they relate to other parts of the installation. If none of 1 through 7 exist already then you must install at least one of the items 4 through 8.





 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
= $ =

if there are multiple,
approved type of grounding electrodes present at a site,
then they must all be bonded together [ RE: Article 250.50,
'08 NEC ].

= $ =

So if you have a ground rod on the truck, does that mean it's "present" and you have to use it :)

Since "present" isn't specifically defined, an AHJ could possibly interpert it that way.


Steve
 

Gregg Harris

Senior Member
Location
Virginia
Occupation
Electrical,HVAC, Technical Trainer
So if you have a ground rod on the truck, does that mean it's "present" and you have to use it :)

Since "present" isn't specifically defined, an AHJ could possibly interpert it that way.


Steve

"Present" as present in the installed system. I do not believe or could possibly conceive that an AHJ would even consider your thought pattern.
 

kwired

Electron manager
Location
NE Nebraska
"Present" as present in the installed system. I do not believe or could possibly conceive that an AHJ would even consider your thought pattern.

But some idiot somewhere will think an abandoned ground rod still in the dirt from a previous installation needs to be connected because it is "present":p
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
But some idiot somewhere will think an abandoned ground rod still in the dirt from a previous installation needs to be connected because it is "present":p

Dig down 2" and cut an inch off. Now it's no longer an electrode. :roll:
 