We are in a rehabilitation project where the existing transformer is 500 kva & loaded by 40% only of its capacity. We are going to replace the existing breakers and fuses. Can we size the main breaker (frame) after transformer by 125% of the transformer capacity & 125% of 40% XFMR (Trip)?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The code only sets the maximum size of the transformer OCPD, it does not set a minimum. You will have no problem on the secondary side by using smaller OCPD, but if you try to reduce the primary side, by that much, the OCPD will probably open when you energize the transformer.
 
Last edited:

m sleem

Exemplary Сasual Dating - Genuine Females
Location
Usa
Occupation
Health
The code only sets the maximum size of the transformer OCPD, it does not set a minimum. You will have no problem on the secondary side by using smaller OCPD, but if you try to reduce the primary side, by that much, the OCPD will probably open when you energize the transformer.
Fine, & would cable's ampacity match the ampere trip?
 