    I recently ran across a code ? that i can't get the same answer to it goes
    20apartments@ 900 sq ft. 3va per sq ft lighting load and 11kw range in each
    what is the total lighting and appliance load for each apt.
    the correct answer is 11945 VA
    how did they come to this answer

    #2
    Originally posted by springriverrat01 View Post
    I recently ran across a code ? that i can't get the same answer to it goes
    20apartments@ 900 sq ft. 3va per sq ft lighting load and 11kw range in each
    what is the total lighting and appliance load for each apt.
    the correct answer is 11945 VA
    how did they come to this answer
    3va/sf * 900sf [COLOR=#ffffff]................[/COLOR]= 2700va
    2 S.A circuit @ 1500va ea = 3000va
    Subtotal[COLOR=#ffffff].........................[/COLOR]= 5700va

    From 220.42
    First 3000va @ 100%......= 3000va
    Remaining 2700va @ 35%= 945va
    From 220.55
    Range[COLOR=#ffffff]............................[/COLOR]= 8000va
    Total[COLOR=#ffffff]..............................[/COLOR]= 11945va

    Comment


      #3
      Originally posted by david luchini View Post
      3va/sf * 900sf [COLOR=#ffffff]................[/COLOR]= 2700va
      2 S.A circuit @ 1500va ea = 3000va
      Subtotal[COLOR=#ffffff].........................[/COLOR]= 5700va

      From 220.42
      First 3000va @ 100%......= 3000va
      Remaining 2700va @ 35%= 945va
      From 220.55
      Range[COLOR=#ffffff]............................[/COLOR]= 8000va
      Total[COLOR=#ffffff]..............................[/COLOR]= 11945va
      I guess they assume a common laundry. I hate questions like that
      They say I shot a man named Gray and took his wife to Italy