Do we have conflict here ?

695.3(d)(2) Connection. A tap ahead of the generator disconnecting
means shall not be required. [20:9.6.1.2]

695.4(A) Direct Connection. The supply conductors shall directly
connect the power source to either a listed fire pump
controller or listed combination fire pump controller and
power transfer switch.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I don't think so. Notice on 695.4 it references "A" or "B".
695.3(d)(2) discussed the generator as an alternate supply.
695.4 discusses how the supply conductors terminate. They can comply with A and terminate on a listed controller or with B and follow the guidelines.
 

m sleem

Exemplary Сasual Dating - Genuine Females
Location
Usa
Occupation
Health
I don't think so. Notice on 695.4 it references "A" or "B".
695.3(d)(2) discussed the generator as an alternate supply.
695.4 discusses how the supply conductors terminate. They can comply with A and terminate on a listed controller or with B and follow the guidelines.

I would think better if NEC add the 695.3(d)(2) as exception of 695.4(a) since the power source is general word.
 

m sleem

Exemplary Сasual Dating - Genuine Females
Location
Usa
Occupation
Health
I don't think so. Notice on 695.4 it references "A" or "B".
695.3(d)(2) discussed the generator as an alternate supply.
695.4 discusses how the supply conductors terminate. They can comply with A and terminate on a listed controller or with B and follow the guidelines.
Would you mean when the generator is prime not standby we could tape ahead of the generator disconnecting means?
 