thanks Augie, that's exactly what I was asking. When you say "There are other ways to connect at the pipe that would allow you to hit it first." could you elaborate?
Thanks
I do not see where it makes any difference which one you attach to first short of creating a weak link. The gas pipe can be terminated on 4 different location.
Now if the gas pipe has CSST and the service is 200 amps or larger then the bonding jumper would need to be a # 4 copper and that could not land on the ground rod that has the # 6.
(B) Other Metal Piping. If installed in, or attached to, a building or structure, a metal piping system(s), including gas piping, that is likely to become energized shall be bonded to the service equipment enclosure; the grounded conductor at the service; the grounding electrode conductor, if of sufficient size; or to one or more grounding electrodes used. The bonding conductor(s) or jumper(s) shall be sized in accordance with
250.122, using the rating of the circuit that is likely to energize the piping system(s). The equipment grounding conductor for the circuit that is likely to energize the piping shall be permitted to serve as the bonding means. The points of attachment of the bonding jumper(s) shall be accessible.