I am a PE and have been asked to provide drawings for a stage performance. The customer says that the industry standard is to run SO type cable in Checkers Yellow Jacket. This separates the three phase cables by a little bit. There is a common lid, so I suppose it would be considered in a single raceway. He says the 4/0 cable is rated for 400A this way.
SO cable is in the 2008 NEC in table 400.5(B). I don't know where he's coming from. This is a three phase service. 4/0 appears to me to have a maximum rating under the circumstances of 316A.
I talked to him and some other people who have experience in stage productions - and they do truly seem to have experience - and they seem extremely confident that 4/0 cable is rated for 400A in this application.
I'm wondering if any of you can shed light on this.
While I'm at it - I will have two separate generators - one for light and one for sound, and will also have four light generators. The light generators don't need a ground rod. But both the other generators will. Both will serve the same stage. They are not paralleled.
I am wanting to connect the grounds on the two generators. If you have a separately derived transformer, you bond that to the building grounding system. Just not to any neutrals. Seems like it would be safest to have these two generator grounds bonded even though they are separate systems since they serve the exact same area. Any comments on that?
Thank you in advance for your help.
SO cable is in the 2008 NEC in table 400.5(B). I don't know where he's coming from. This is a three phase service. 4/0 appears to me to have a maximum rating under the circumstances of 316A.
I talked to him and some other people who have experience in stage productions - and they do truly seem to have experience - and they seem extremely confident that 4/0 cable is rated for 400A in this application.
I'm wondering if any of you can shed light on this.
While I'm at it - I will have two separate generators - one for light and one for sound, and will also have four light generators. The light generators don't need a ground rod. But both the other generators will. Both will serve the same stage. They are not paralleled.
I am wanting to connect the grounds on the two generators. If you have a separately derived transformer, you bond that to the building grounding system. Just not to any neutrals. Seems like it would be safest to have these two generator grounds bonded even though they are separate systems since they serve the exact same area. Any comments on that?
Thank you in advance for your help.