If a seating pavilion is going to have lights in it does the NEC require there to be outlets as well? I can't find anything that clearifies.
 

north star

Senior Member
Location
inside Area 51
= =

Please define clearly what you are calling a "Pavillion" !
Is it enclosed or fully open, ...partially open / partially
enclosed ?....What construction standards are being
used, if any ?

No requirements for receptacles to be installed
outdoors, but if they are, ...then there are requirements
for protection.

"If a seating pavilion is going to have lights in it does the NEC require
there to be outlets as well?"
The lights that you mentioned are outlets !
See Article 100 - Definitions.

= =
 