    MC cable - Burial Depth

    Which Column does MC cable fall under in Table 300.5 or Table 300.50 ?

    #2
    Column 1 is for "Direct Burial Cables or Conductors" but it could possibly also fall under Columns 4 or 5.
    Rob

    Moderator

    All responses based on the 2017 NEC unless otherwise noted

    Comment


      #3
      I have a 480/277V feeder, would this make any difference ?

      Comment


        #4
        That would eliminate using columns 4 & 5.
        Rob

        Moderator

        All responses based on the 2017 NEC unless otherwise noted

        Comment


          #5
          OK thanks for your help, this leaves only Column 1.

          Comment


            #6
            Originally posted by Ranger86 View Post
            Which Column does MC cable fall under in Table 300.5 or Table 300.50 ?
            300.50 is in Part III of Article 110 and is over 600 volt systems. The system voltage tells you what table to use.
            Don, Illinois
            (All code citations are 2017 unless otherwise noted)

            Comment


              #7
              To the OP, I believe it's a violation of 330.12 (on the 08 code) to bury ordinary mc cable?
              son you finally got it made

              Comment


                #8
                I assume he's using this stuff:
                Attached Files

                Comment


                  #9
                  Originally posted by plumb bob View Post
                  To the OP, I believe it's a violation of 330.12 (on the 08 code) to bury ordinary mc cable?
                  Not all MC is created equal, some of it is designed for direct burial or wet/corrosive locations, and that section even addresses this fact.
                  I live for today, I'm just a day behind.

                  Comment