Let's say there's a branch circuit protected by a 20 ampere breaker. A 12/2 (with ground) NM cable runs from the breaker, out to a switch box. Inside the switch box, the ungrounded conductor of the 12/2 cable is connected to one terminal of the switch. A 14/2 (with ground) NM cable runs between the switch box, and a box where a lighting fixture will be installed. The ungrounded conductor of the 14/2 cable connects to the other terminal of the switch, the grounded and grounding conductors from the 12/2 cable are connected to the grounded and grounding conductors of the 14/2 cable. Also everything is properly grounded at all locations.
The light fixture being installed is a 3 bulb fixture, rated at a maximum of 180 Watts.
Would the use of the 14/2 cable be a violation of NEC? If in the switch box another 12/2 cable was connected to extend the circuit, does this change anything?