    Feeder from a generator

    I am feeding a trailer, (pull behind. ) From a 60 amp generator to a 60 amp panel. Separate ground and neutral from generator to panel, does the ground and neutral have to be separate and why and what section in the nec

    Sent from my SM-G360P using Tapatalk

    #2
    Please review 250.20, 250.30, 250.34 and 250.35.
    If the generator is a SDS, then you need a SBJ, where depends on the generator OCPD location.
    With the generator, just like a service, you need grounding, bonding,a bonding jumper, and a grounding electrode system if its a SDS.
    Moderator-Washington State
    Ancora Imparo

    Comment


      #3
      Can someone recommend a grounding electrode idea for this trailer, has a 60 amp generator feeding a 60 amp panel, how would you do the grounding

      Sent from my SM-G360P using Tapatalk

      Comment


        #4
        Originally posted by Joseph mulherin View Post
        Can someone recommend a grounding electrode idea for this trailer, has a 60 amp generator feeding a 60 amp panel, how would you do the grounding

        Sent from my SM-G360P using Tapatalk
        You can always drive a ground rod, but IMO your question can't be answered with the information you have given. Did you review the code sections Tom posted.
        If Billy Idol is on your playlist go reevaluate your life.

        Comment