Hi everyone:

I recently saw a low voltage dry type transformer that feeds at least 3 different loads, one panel board and two machines, the strange thing is that all feeders are connected inside the transformer, I don't know if they are directly connected to the transformer's secondary terminals or if there are cable splices inside his enclosure. Any of these situations are NEC compliant?

Best regards
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Could be compliant & relative common.. If all the secondary conductors meet the 240.21(C) rules and the transformer is protected per 450.3.
 