Interruptable for ac condenser at residential house single dwelling

Status
Not open for further replies.

timtom58

Member
Location
allen park mi.
I know disconnects are to be grouped together, but if there is one at Interruptable meter , then wire goes thru the basement to other side of house to condenser location where the other disconnect is, is that ok? The one at meter is nonfused, and the one at condenser is fused. Also does anyone have a code referance for that rule,...off the top of your head ?

Sent from my GT-N8013 using Tapatalk
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
One service (drop or lateral) and two meters ?
Where are the disconnects for the non-interruptible service meter ?

IN addition to "grouping", it sounds like a couple of violations. If the disconnect at the meter is non-fused I would not classify it as the "service disconnect" since the OCP is not there (230.91).
The conductors traveling thru the house without OCP would be a violation of 230.70(A)(1)
 