Phase conductors and derating

Status
Not open for further replies.

Shockedby277v

Senior Member
Location
Michigan
I know that you use to be able to run all of a phase into a single pipe if the entire run was PVC with no metal but I don't if the '14 code changed anything with it. I can't find the code article. Here's what I want to do.

I would like to run to my transformer from the service with 4 - 6" pipes (PVC). A pipe for each phase and neutrals. Vs running 10 - 4" pipes. There is question #1.

My second question is. Do I need to derate these? I plan on running 10 - 600 Cu per phase for a 4000 amp service.

Thanks
 

Carultch

Senior Member
Location
Massachusetts
I know that you use to be able to run all of a phase into a single pipe if the entire run was PVC with no metal but I don't if the '14 code changed anything with it. I can't find the code article. Here's what I want to do.

I would like to run to my transformer from the service with 4 - 6" pipes (PVC). A pipe for each phase and neutrals. Vs running 10 - 4" pipes. There is question #1.

My second question is. Do I need to derate these? I plan on running 10 - 600 Cu per phase for a 4000 amp service.

Thanks

Given 10 CCC's in a single conduit, you do have to derate for bundling, and possibly with a basic derate for ambient temperature as well.
 

kwired

Electron manager
Location
NE Nebraska
I know that you use to be able to run all of a phase into a single pipe if the entire run was PVC with no metal but I don't if the '14 code changed anything with it. I can't find the code article. Here's what I want to do.

I would like to run to my transformer from the service with 4 - 6" pipes (PVC). A pipe for each phase and neutrals. Vs running 10 - 4" pipes. There is question #1.

My second question is. Do I need to derate these? I plan on running 10 - 600 Cu per phase for a 4000 amp service.

Thanks
See 300.3(B) and 310.10(H) for rules on parallel conductors.

Yes you can run all one phase in one non metallic raceway in your application. You still need to adjust ampacity when there is more then 3 current carrying conductors in a raceway though, and 10 conductors gives you a 50% adjustment - which would probably hurt your wallet on your project those 600 Cu are only good for 237.5 amps with 10 in a raceway, if you can get to 9 conductors then 70% adjustment applies, but would still need to be much larger conductors to get to 4000 amps.
 