Dishwasher GFCI Arc

Status
Not open for further replies.

Vmadden

Member
Location
Baltimore
We recently wired a dishwasher with a separate 20 amp circuit and connected it to a combination GFI Arc breaker.

We installed a wall switch below the sink as instructed by other inspectors.

My inspector wants my to install a GFI receptacle below the sink and an appliance cord for the dishwasher.

He will not allow a single pole switch under the sink. When I told him we already had GFI protection at the breaker he said he would not allow this, it must be a GFI receptacle under the sink.

What do you guys think. I think the code also allows a breaker lock to be used as a disconnect. The kind of breaker lock one can put a lock on.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
A breaker lock is acceptable as long as it remains attached to the panel when the lock is open.
If you have a GFCI breaker you do not need to use a GFCI receptacle if you choose to use a cord and plug for the disconnect.
He cannot insist on a physical switch at the DW.
 