Electrician
Whether to the earth or to the grid, fault path will seek all resistances - but back to the Xfmr (via the GEC) will be the least resistance path for solidly grounded Wye systems which is usually around 1 ohm or less. If you have a High Resistance Ground on the Delta-Wye Xfmr that's a different story.

Not true.

JAP>
 

kmh

Member
Whether to the earth or to the grid, fault path will seek all resistances - but back to the Xfmr (via the GEC) will be the least resistance path for solidly grounded Wye systems which is usually around 1 ohm or less. If you have a High Resistance Ground on the Delta-Wye Xfmr that's a different story.

The GEC is important for reasons I won't go into here. But the EGC is what's really needed to clear a ground fault in a timely manner. So I disagree with your statement "but back to the Xfmr (via the GEC)." Ground fault current gets back to the xfmr primarily via neutral bonded to the EGC.
 

Dale001289

Senior Member
Location
Georgia
The GEC is important for reasons I won't go into here. But the EGC is what's really needed to clear a ground fault in a timely manner. So I disagree with your statement "but back to the Xfmr (via the GEC)." Ground fault current gets back to the xfmr primarily via neutral bonded to the EGC.


If a fault occurs within the circuit, on the conduit or at the end device, it will travel via the neutral/EGC back to Xfmr - this represents the vast majority of faults--But when a fault hits the earth or grid remote from the EGC, it wont simply disappear into the earth - it will go back to the Xfmr.
 

kmh

Member
If a fault occurs within the circuit, on the conduit or at the end device, it will travel via the neutral/EGC back to Xfmr - this represents the vast majority of faults--But when a fault hits the earth or grid remote from the EGC, it wont simply disappear into the earth - it will go back to the Xfmr.

Hopefully everyone in this forum realizes current does not just disappear into the earth.
 

jap

Senior Member
Occupation
Electrician
If a fault occurs within the circuit, on the conduit or at the end device, it will travel via the neutral/EGC back to Xfmr - this represents the vast majority of faults--But when a fault hits the earth or grid remote from the EGC, it wont simply disappear into the earth - it will go back to the Xfmr.

When a fault occurs to normally non current carrying paths that are conductive, that current travels via the EGC back to the Grounded Conductor at the transformer if wired correctly, and yes, this represents one type of fault condition.

Again. A lightning strike is not a fault.

I've never seen a transformer or overcurrent protection device ahead of a lightning strike....... have you? :)

Yes, a lightning strike does in fact simply disappear into the earth.
You can't stop a lightning strike by any amount of ground rods or grids.

If what you were saying were true, about a lightning strike traveling back up the GEC to the Grounded Conductor on a transformer in close proximity, lightning would destroy a ton of transformers each time one decided to strike the earth.

That's simply not the case.

JAP>
 

jap

Senior Member
Occupation
Electrician
True. Fault that goes into the ground must come out. It does not 'disperse' into the unknown earth.

Where does it come out at?

If a strike occurs in Colorado on a stormy day, does it come back up out of the ground in China and jump back up into the sky on a perfectly beautiful day ?

JAP>
 

jap

Senior Member
Occupation
Electrician
Hopefully everyone in this forum realizes current does not just disappear into the earth.

Where does it go?

So a lightning strike that hits the earth comes back up out of the ground,goes back up all of our Grounding electrode conductors to the Neutral point of all of our transformers, and that's what stops it?

I think not.

JAP>
 

Dale001289

Senior Member
Location
Georgia
Where does it come out at?

If a strike occurs in Colorado on a stormy day, does it come back up out of the ground in China and jump back up into the sky on a perfectly beautiful day ?

JAP>

I used to think lightning would dissipate into the earth too - but it doesn't work that way. It will seek a path to come out of the earth - it seeks ALL resistances, the sum of which equals the path of least resistance. That's why the people Hong Kong will never see a lightning strike in the US.
 

kmh

Member
I used to think lightning would dissipate into the earth too - but it doesn't work that way. It will seek a path to come out of the earth - it seeks ALL resistances, the sum of which equals the path of least resistance. That's why the people Hong Kong will never see a lightning strike in the US.

Lightning is a whole different story than ground fault current. Charge a capacitor with DC voltage, then take the voltage connection away. Now jumper one side of the capacitor to the other. You'll get momentary current flow as the charges equalize. That's lightning. It's two opposite charges equalizing.
 

Dale001289

Senior Member
Location
Georgia
Lightning is a whole different story than ground fault current. Charge a capacitor with DC voltage, then take the voltage connection away. Now jumper one side of the capacitor to the other. You'll get momentary current flow as the charges equalize. That's lightning. It's two opposite charges equalizing.


True, but has nothing to do with this conversation -
 

jap

Senior Member
Occupation
Electrician
Lightning is a whole different story than ground fault current. Charge a capacitor with DC voltage, then take the voltage connection away. Now jumper one side of the capacitor to the other. You'll get momentary current flow as the charges equalize. That's lightning. It's two opposite charges equalizing.

And that momentary current flow is just that.
A current flow.

Not a ground fault.


JAP>
 

Dale001289

Senior Member
Location
Georgia
And that momentary current flow is just that.
A current flow.

Not a ground fault.


JAP>

Call it what you want.... but in a major lightning strike you could have hundreds of thousands of Amps/Volts hitting the earth — where does it go after it hits the earth?
Answer: it travels horizontally thru the earth seeking a path to come out - and where is the least resistance? Is it a tree? A fence?
Remember the transformer XO is at very low resistance



Sent from my iPhone using Tapatalk
 

jap

Senior Member
Occupation
Electrician
Call it what you want.... but in a major lightning strike you could have hundreds of thousands of Amps/Volts hitting the earth — where does it go after it hits the earth?
Answer: it travels horizontally thru the earth seeking a path to come out - and where is the least resistance? Is it a tree? A fence?
Remember the transformer XO is at very low resistance



Sent from my iPhone using Tapatalk


For the Lightning strike to hit the earth, or a strike from the earth to the clouds, that portion of the cloud to earth or earth to cloud path had to be the path of least resistance to begin with.

Otherwise, the lightning strike would have never happened in the first place.

JAP>
 

Dale001289

Senior Member
Location
Georgia
For the Lightning strike to hit the earth, or a strike from the earth to the clouds, that portion of the cloud to earth or earth to cloud path had to be the path of least resistance to begin with.

Otherwise, the lightning strike would have never happened in the first place.

JAP>[/QUOTE

:happysad::blink:
 

jap

Senior Member
Occupation
Electrician
If a lightning strike hit out in the middle of a field with nothing electrical near the strike location, I find it hard to believe that it would travel through the earth until it found the XO terminal of a transformer for it to come back out of the ground.

Why would it search for that point?

JAP>
 

jap

Senior Member
Occupation
Electrician
For the Lightning strike to hit the earth, or a strike from the earth to the clouds, that portion of the cloud to earth or earth to cloud path had to be the path of least resistance to begin with.

Otherwise, the lightning strike would have never happened in the first place.

JAP>[/QUOTE

:happysad::blink:

Why the head shake ?

JAP>
 

kmh

Member
Call it what you want.... but in a major lightning strike you could have hundreds of thousands of Amps/Volts hitting the earth — where does it go after it hits the earth?
Answer: it travels horizontally thru the earth seeking a path to come out - and where is the least resistance? Is it a tree? A fence?
Remember the transformer XO is at very low resistance

Oooh, gotta disagree with that! A charge of one polarity accumulates in the clouds ( I think it's positive, but Google it yourself.) A charge of the opposite polarity accumulates in the ground. Eventually the potential difference is so high that the atmosphere ionizes creating a conductive path between the two opposite charges, thereby equalizing the potential difference. Current does not need to flow any farther than that. It's merely a matter of positive charges meeting negative charges to reach equilibrium. And this has nothing to do with returning ground fault current to a transformer XO.
 