    Underground feeder junction box

    I am installing a 350' long run of PVC, 240V single phase feeder underground.
    Am I permitted to put a quazite pull box somewhere in that run? There will be no splices in the pull box.

    #2
    Yes, there is nothing in the code that either requires or prohibits that box.
    Don, Illinois
    (All code citations are 2017 unless otherwise noted)

    Comment


      #3
      You can even bury it if you can comply with the exception in 314.29.
      Rob

      Moderator

      All responses based on the 2017 NEC unless otherwise noted

      Comment


        #4
        Originally posted by don_resqcapt19 View Post
        Yes, there is nothing in the code that either requires or prohibits that box.
        That's what I thought, just wanted to make sure I wasn't missing something.
        Thank you