I have 240V load for cooking in kitchen single phase but my service is 208V/120V. I am going to ise 208V single phase to 240V single buck boost Larson MT-BBT-208V-240V-23.4A transformer. However, what NEC Article section talks about grounding this sort of transformer?

Sent from my SM-G935U using Tapatalk
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have 240V load for cooking in kitchen single phase but my service is 208V/120V. I am going to ise 208V single phase to 240V single buck boost Larson MT-BBT-208V-240V-23.4A transformer. However, what NEC Article section talks about grounding this sort of transformer?

Sent from my SM-G935U using Tapatalk
Ok so I found 450.5 but that says connected to 3 phase ungrounded system and its for autotransformer but I have buck boost transformer. Other than that Article 250.30 but thats for separtely derived system not for buck bost transformer. So. I am still not sure what to use. Manufacturer instruction say ground per NEC. Its confusing.

Sent from my SM-G935U using Tapatalk
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
Ok so I found 450.5 but that says connected to 3 phase ungrounded system and its for autotransformer but I have buck boost transformer. Other than that Article 250.30 but thats for separtely derived system not for buck bost transformer. So. I am still not sure what to use. Manufacturer instruction say ground per NEC. Its confusing.

Sent from my SM-G935U using Tapatalk

Try 250.110
 