Is there any code rule that prohibits that a cable tray holding medium voltage cables be installed below (less height) than a cable tray for low voltage cables? Thanks in advance for your help. :)
 

iceworm

Curmudgeon still using printed IEEE Color Books
Location
North of the 65 parallel
Occupation
EE (Field - as little design as possible)
None I know of.

I've seen installations that have three trays:
MV (13.8kv)
LV (480V)
Instrument
Although they usually are stacked in descending order I've never heard of a code rule.

the worm
 

mendizi

Member
Location
Colombia
Thanks iceworm. A colleague tell me about IEEE standards 422 and 525 for Generation Facilities and Substations respectively, where it is explicit that stacked cable trays should be arranged by descending voltagelevels, with the higher voltage at the top, but apart from that standards any mandatory rule seems nonexistent.
 