Distance restriction from main service disconnect to MLO sub panel (residential)

Status
Not open for further replies.

tadavidson

Senior Member
Location
Georgia
Occupation
Electrical Contractor
a homeowner wiring his own home recently asked me was there an issue that his main disconnect is 175 ft from his panel inside his home it is an mlo 30 position.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
ass-uming a 200 amp panel, 4/0 AL at 100 amps worth of load he's looking at VD of 14.
I would consider upsizeing my feeder, but no Code issue.
 