408.35 Number of Overcurrent devices on one panelboard

Status
Not open for further replies.

davedottcom

Senior Member
Need to add a (2-pole) surge protector in a 40-space panel that is Full.

Installing(2) tandem breakers and the Surge protector shouldn't be a violation since there is still only 40 over current devices.

A surge protector isn't an over current device it's an over Voltage device!!!

Right!?
 

davedottcom

Senior Member
I agree with the OP. The question is who else is going to look at it and approve it? Will tandems work in the panel?

If (2) Non-Circuit-Limiting Tandem breakers are installed there will still be only 40 over current devices and (1) 2-pole Surge protector.
 

davedottcom

Senior Member
I must admit I don't know how that answered or addressed my questions.

Well, it's a Sq-D QO panel so yes it definitely accepts NCL-tandem breakers. The reason the panel will be completely FULL is; I'm installing the 40th circuit! :D Yes, there will be an inspection but I'm not just trying to get it to "pass inspection", I'm trying to find out if it's "NEC compliant". 2 Very different things! :D
 

davedottcom

Senior Member
The reason the panel will be completely FULL is; I'm installing the 40th circuit! :D

Correction! I'm installing the 39th circuit, not the 40th. Currently there are 38 circuits/spaces used in a 40 space panel. I'm adding 1 more single pole and the surge protector requires 2 spaces although it's not an over current device.
 

davedottcom

Senior Member
I'm confused how many spaces does the panel have?

lol... ok...

It's a 40 space / 40 circuit QO panel
It currently has 38 spaces used (Circuit breakers)
That leaves 2 spaces for the surge protector
The surge protector is not an over current device so there is still only 38 circuits but no more room for the 39th circuit.
I want to replace 1 single pole breaker with a NCL QO tandem for the 39th circuit.
Technically, I could do this again for a 40th circuit someday and there would still only be 40 over current devices and a 2-pole surge protector.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
lol... ok...

It's a 40 space / 40 circuit QO panel
It currently has 38 spaces used (Circuit breakers)
That leaves 2 spaces for the surge protector
The surge protector is not an over current device so there is still only 38 circuits but no more room for the 39th circuit.
I want to replace 1 single pole breaker with a NCL QO tandem for the 39th circuit.
Technically, I could do this again for a 40th circuit someday and there would still only be 40 over current devices and a 2-pole surge protector.

The number of OCPD's is irrelevant, the issue may be that the panel is not listed for use with tandem circuit breakers.
 

Buck Parrish

Senior Member
Location
NC & IN
Chances are some of the circuits may only have one outlet on it. Or perhaps a light or two maybe a door bell transformer. You can pig tail those in the panel to make an extra space or two.
 

davedottcom

Senior Member
Chances are some of the circuits may only have one outlet on it. Or perhaps a light or two maybe a door bell transformer. You can pig tail those in the panel to make an extra space or two.

Yes very true.

Ok... I'm going to say something I'm probably going to regret but... aren't Square-D breakers permitted to have 2-wires on their terminals? 1 on each side of the screw. (They sure look like they are!)
 

MAC702

Senior Member
Location
Clark County, NV
Ok... I'm going to say something I'm probably going to regret but... aren't Square-D breakers permitted to have 2-wires on their terminals? 1 on each side of the screw. (They sure look like they are!)

Depends on if you are asking Square D, the NEC, the AHJ, a real electrician (all of whom say yes), or a Home Inspector.
 

kwired

Electron manager
Location
NE Nebraska
The number of OCPD's is irrelevant, the issue may be that the panel is not listed for use with tandem circuit breakers.
+1

Yes very true.

Ok... I'm going to say something I'm probably going to regret but... aren't Square-D breakers permitted to have 2-wires on their terminals? 1 on each side of the screw. (They sure look like they are!)
typical 30 amp and less are designed to accept two conductors on their terminals.

Depends on if you are asking Square D, the NEC, the AHJ, a real electrician (all of whom say yes), or a Home Inspector.
HI's can't seem to figure this one out.
 