Opening a disconnect in the closed position

Status
Not open for further replies.

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
That is not in the NEC. It may be in the product standard, but I am not sure.

As Don said it's not in the code forbidding it.
I know at one time you could open them in the closed position by turning a screw on the side that over rode the door locks and would let you open it in the closed position.
I don't think you can do that now. May be a UL thing or OSHA thing.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
NFPA 79 (the standard for industrial machine controls) requires that doors be interlocked with a disconnecting device so that you cannot enter an enclosure without first killing power and any defeater mechanism requires a tool to operate, implying that whomever defeats it is a "qualified worker" in a facility.

The NEC has few requirements for this in Low Voltage, hence the existence of fused pull-outs as disconnect devices. But there are a few exceptions; bus duct disconnects (368.239), and Medium Voltage equipment MUST be interlocked.
 