210.8(B) - Other than dwelling units

Status
Not open for further replies.

ngd4130

Member
I believe the NEC is specific referring to the type of devices needed to be backed by GFCI protection in non-dwelling kitchens. However, if the appliance was direct wired through a fused or non-fused disconnect switch, would the GFCI requirement be lifted? The definition for a 'receptacle' appears to be for the 'mating' of devices. Some discussion would help to provide options for these applications. Thank you.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The gfci protection relates to receptacles not direct wire equipment

(B) Other Than Dwelling Units. All single-phase receptacles
rated 150 volts to ground or less, 50 amperes or less and three phase
receptacles rated 150 volts to ground or less,
100 amperes or less installed in the following locations shall
have ground-fault circuit-interrupter protection for personnel.
 