    Two switchboards

    I have two service laterals from one utility transformer. One goes to swbd #1 and second goes to swbd #2.

    In swbd #1 I have gnd bus and neutral bus, main bonding jumper, from neutral bar GECs to bldg steel, underground metal pipe, gnd rods.

    Just so I can tie all building GE together, can I tie another GEC from swb#1 neutral bar and tie to Gnd bus of swbd #2 that has main bonding jumper? Code allows that? Or I need main bus bar outside with conductors going to GE and one conductor going to Swbd #1 and second conductor going to swbd #2?

    Sent from my SM-G935U using Tapatalk

    #2
    Originally posted by hhsting View Post
    I have two service laterals from one utility transformer. One goes to swbd #1 and second goes to swbd #2.

    In swbd #1 I have gnd bus and neutral bus, main bonding jumper, from neutral bar GECs to bldg steel, underground metal pipe, gnd rods.

    Just so I can tie all building GE together, can I tie another GEC from swb#1 neutral bar and tie to Gnd bus of swbd #2 that has main bonding jumper? Code allows that? Or I need main bus bar outside with conductors going to GE and one conductor going to Swbd #1 and second conductor going to swbd #2?

    Sent from my SM-G935U using Tapatalk
    IIRC, you can tie it to the first swbd ground bus if it is a ground bar that is at least 1" x 2".
    Bob

    Comment


      #3
      Are these switchboards grouped? Are you sure they are service laterals off the transformer? Something doesn't seem right.
      Ethan Brush - East West Electric. NY, WA. MA

      "You can't generalize"

      Comment


        #4
        Originally posted by electrofelon View Post
        Are these switchboards grouped? Are you sure they are service laterals off the transformer? Something doesn't seem right.
        Its brand new building so I can see it. I have two sets of service conductors from one utility transformer: one goes to building swbd #1 and other swbd #2. Swbd #2 has building ats/controller fire pump load and breakers to other motor load related to fire pump so no both are not grouped in one location.

        Sent from my SM-G935U using Tapatalk

        Comment


          #5
          The way I read 250.64(D), it is not allowed. A grounding electrode conductor must be brought from each service disconnect and terminated to the grounding electrodes or a common grounding electrode conductor sized for both disconnects or a bar as specified in 250.64(D)(1) and reference by petersonra above.
          Removal of 1 switchboard can not interrupt the path of the other to the grounding electrode system.
          At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

          Comment


            #6
            Originally posted by augie47 View Post
            The way I read 250.64(D), it is not allowed. A grounding electrode conductor must be brought from each service disconnect and terminated to the grounding electrodes or a common grounding electrode conductor sized for both disconnects or a bar as specified in 250.64(D)(1) and reference by petersonra above.
            Removal of 1 switchboard can not interrupt the path of the other to the grounding electrode system.
            I dont think 250.64(D) applies. 250.64(D) which says if a building is supplied by a service with two or more disconnecting. So if you have one service with muiltiple service disconnect then 250.64(D) applies.

            I have two services from one utility transformer.

            Comment


              #7
              As I read 230.2 what you have is considered one service.
              At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

              Comment


                #8
                Originally posted by augie47 View Post
                As I read 230.2 what you have is considered one service.
                Ah 230.2 you mean when it says 1/0 AWG and larger running to same location and connected together at their supply end but not connected together at their load end considered one service.
                Last edited by augie47; 01-24-19, 07:55 PM.

                Comment


                  #9
                  Yes. and if you want to consider it as (2) services, to me, 250.64(F) would require the electrode conductor be run directly to the electrodes or the previously described "plate"
                  At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

                  Comment


                    #10
                    Originally posted by hhsting View Post
                    Ah 230.2 you mean when it says 1/0 AWG and larger running to same location and connected together at their supply end but not connected together at their load end considered one service.

                    Yes. and if you wantt o consider it as (2) services, to me, 250.64(F) would require the electrode conductor be run directly to the electrodes or the previously described "plate"
                    Ok 230.2 says for the purpose of 230.40 exception no.2 only, ungrounded sets of conductors 1/0 awg and larger, running to the same location and connected at their supply end but not connected together at their load end shall be considered one service.

                    See for the purpose of 230.40 exception no. 2 in their.

                    Is that an extension of 230.40 exception no.2 i.e an addition to or is that implying if i have two to six disconnect grouped but not connected at load end but connected at supply end with 1/0awg or larger is one service? My swbd are not grouped.

                    Comment


                      #11
                      Originally posted by hhsting View Post
                      Ok 230.2 says for the purpose of 230.40 exception no.2 only, ungrounded sets of conductors 1/0 awg and larger, running to the same location and connected at their supply end but not connected together at their load end shall be considered one service.

                      See for the purpose of 230.40 exception no. 2 in their.

                      Is that an extension of 230.40 exception no.2 i.e an addition to or is that implying if i have two to six disconnect grouped but not connected at load end but connected at supply end with 1/0awg or larger is one service? My swbd are not grouped.
                      OK, go back to post 9.. two services...
                      At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

                      Comment


                        #12
                        Originally posted by augie47 View Post
                        Yes. and if you want to consider it as (2) services, to me, 250.64(F) would require the electrode conductor be run directly to the electrodes or the previously described "plate"
                        The plate in my case is the neutral bar in swbd #1. 250.64(F) does not say it cannot be the same busbar as in the switchboard so as long as the neutral busbar in swbd #1 is 0.25 in x 2 in wide and in accessible location. Switchboard neutral bus bar is accessible.

                        I dont see anywhere else in code above cannot be done. No?

                        Sent from my SM-G935U using Tapatalk

                        Comment


                          #13
                          I find that to be a real "stretch" of the "common buss" wording but obviously we are of a different opinion.
                          You have mine in that is it's a violation.
                          Perhaps there will be more Forum input.
                          At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

                          Comment


                            #14
                            Originally posted by hhsting View Post
                            The plate in my case is the neutral bar in swbd #1. 250.64(F) does not say it cannot be the same busbar as in the switchboard so as long as the neutral busbar in swbd #1 is 0.25 in x 2 in wide and in accessible location. Switchboard neutral bus bar is accessible.

                            I dont see anywhere else in code above cannot be done. No?

                            Sent from my SM-G935U using Tapatalk
                            why don't you just go from 2nd service to building steel. And use building steel to bond any other electrodes that are part of the grounding electrode system. If these two laterals supplied two grouped service disconnects the NEC stipulates a tap to a common grounding electrode conductor.

                            If you do not do this for grouped disconnects why would you do this for two separate service disconnects

                            Comment


                              #15
                              Originally posted by david View Post
                              why don't you just go from 2nd service to building steel. And use building steel to bond any other electrodes that are part of the grounding electrode system. If these two laterals supplied two grouped service disconnects the NEC stipulates a tap to a common grounding electrode conductor.

                              If you do not do this for grouped disconnects why would you do this for two separate service disconnects
                              If I had decision to make I would get busbar separate outside of swbd and have one GEC from swbd #1 , one GEC to swbd #2 to outside busbar and then have bonding jumpers from the busbar to GE.

                              But I am being questioned as to the installation of neutral bar as common bus in swbd #1 by the owners where is it in NEC code violation. Its accessible and bonding jumpers are going to GE and GEC come from swbd #2 to swbd #1 neutral bar. It complies per nec 250.64(F)(3) so as long as neutral bar in swbd #1 is 0.25 in by 2 in.
                              Last edited by hhsting; 01-24-19, 10:53 PM.