replacing ceiling light with paddle fan - AFCI required?

Status
Not open for further replies.

JohnE

Senior Member
Location
Milford, MA
If I am replacing a ceiling light in a dwelling unit family room or bedroom, with a paddle fan/ light, does the NEC require this new fan to have AFCI protection? Since this isn't a new outlet, I don't see that adding AFCI protection would be required. Your thoughts? 2017 NEC. To be clear, there is no new wiring. Simply removing the existing light and box, installing fan rated box and fan with light kit. I know there have been many similar discussions, I did some searching, and couldn't find anything closely related.
 

JohnE

Senior Member
Location
Milford, MA
Thank you for the replies. I had a disagreement with an inspector over this. After explaining my interpretation, I haven't heard back from him. I am waiting to hear whether my customer wants to spend the money to add the AFCI protection, or have me appeal the decision to the state, which is a straightforward process that cand take a few months. The repercussion could be having to add AFCI protection to 15 units in a state housing authority property if they don't want me to appeal the decision. (This doesn't affect me financially, if I need to add the AFI's it is billable. The housing authority will ultimately cover it, and eventually at the expense of taxpayer. Albeit it not enough to "matter")
 

kwired

Electron manager
Location
NE Nebraska
Thank you for the replies. I had a disagreement with an inspector over this. After explaining my interpretation, I haven't heard back from him. I am waiting to hear whether my customer wants to spend the money to add the AFCI protection, or have me appeal the decision to the state, which is a straightforward process that cand take a few months. The repercussion could be having to add AFCI protection to 15 units in a state housing authority property if they don't want me to appeal the decision. (This doesn't affect me financially, if I need to add the AFI's it is billable. The housing authority will ultimately cover it, and eventually at the expense of taxpayer. Albeit it not enough to "matter")
Your inspector's supervisor been involved, or is that the part that takes months?

If I had such a situation my inspector would call his supervisor right in front of me, and we likely come to a decision right then and there. If I don't like the decision and don't want to comply, then it gets more complicated.
 

JohnE

Senior Member
Location
Milford, MA
Your inspector's supervisor been involved, or is that the part that takes months?

If I had such a situation my inspector would call his supervisor right in front of me, and we likely come to a decision right then and there. If I don't like the decision and don't want to comply, then it gets more complicated.

There is no supervisor. It's just him. Which is typical in this state, unless you are in one of the larger cities. If we don't get to the point where we see things the same, there are 2 choices. 1. Change it to what he wants, 2. Appeal to the state, which takes a few months. Actually 3 choices. I can do what he wants (to allow the contractor to collect final payment) and still appeal the decision to the state. But this option is only for self-gratification.

I haven't heard back from him in a few days. Hoping he will reconsider.
 

kwired

Electron manager
Location
NE Nebraska
There is no supervisor. It's just him. Which is typical in this state, unless you are in one of the larger cities. If we don't get to the point where we see things the same, there are 2 choices. 1. Change it to what he wants, 2. Appeal to the state, which takes a few months. Actually 3 choices. I can do what he wants (to allow the contractor to collect final payment) and still appeal the decision to the state. But this option is only for self-gratification.

I haven't heard back from him in a few days. Hoping he will reconsider.
IOW any supervisor he has is not electrically qualified to challenge any of his decisions in said area? He certainly got hired by someone even if a board or council, and can also be fired by same, otherwise how did he acquire his monarch?

Apparently no State AHJ or at least laws are written that they can't intervene, or they think they are too busy to care to intervene? Many times State AHJ still has authority over local AHJ's and sets some standards the locals must follow.
 

GerryB

Senior Member
There is no supervisor. It's just him. Which is typical in this state, unless you are in one of the larger cities. If we don't get to the point where we see things the same, there are 2 choices. 1. Change it to what he wants, 2. Appeal to the state, which takes a few months. Actually 3 choices. I can do what he wants (to allow the contractor to collect final payment) and still appeal the decision to the state. But this option is only for self-gratification.

I haven't heard back from him in a few days. Hoping he will reconsider.
Was it a city AHJ or a housing authority inspector? We have them here for section 8 inspections, sometimes require things above the code, like an ungrounded outlet you can't just put in a gfi, you have to run a ground.
 
Last edited by a moderator:

JohnE

Senior Member
Location
Milford, MA
IOW any supervisor he has is not electrically qualified to challenge any of his decisions in said area? He certainly got hired by someone even if a board or council, and can also be fired by same, otherwise how did he acquire his monarch?

Apparently no State AHJ or at least laws are written that they can't intervene, or they think they are too busy to care to intervene? Many times State AHJ still has authority over local AHJ's and sets some standards the locals must follow.

He would typically be hired by the town manager, or board of selectman. But they cannot overrule his professional decision. We have a procedure to appeal his decision to the State Board of Electrical Examiners. I'm hoping it doesn't come to that.

Was it a city AHJ or a housing authority inspector? We have them here for section 8 inspections, sometimes require things above the code, like an ungrounded outlet you can't just put in a gfi, you have to run a ground.

This was the Town wiring inspector, not an inspector from the Housing Authority. I've run into housing and health regulations/ codes that require more than is required by the NEC.
 

GerryB

Senior Member
He would typically be hired by the town manager, or board of selectman. But they cannot overrule his professional decision. We have a procedure to appeal his decision to the State Board of Electrical Examiners. I'm hoping it doesn't come to that.



This was the Town wiring inspector, not an inspector from the Housing Authority. I've run into housing and health regulations/ codes that require more than is required by the NEC.

Our code addresses modifications, extensions, and in 406 replacement receptacles. No mention of luminaires or fans. Guess you'll have to try and point that out to him. You would probably have to protect the whole circuit via a breaker. Could have issues, especially in a housing authority unit. If it's landlord owned they do all their own work and only call the electrician when they can't figure it out or need a permit.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
..Was it a city AHJ or a housing authority inspector? We have them here for section 8 inspections, sometimes require things above the code, like an ungrounded outlet you can't just put in a gfi, you have to run a ground.
..This was the Town wiring inspector, not an inspector from the Housing Authority. I've run into housing and health regulations/ codes that require more than is required by the NEC.

Our Housing inspectors also fail GFCI's protection of 2-wire cables, demanding grounding wire. The culprits are municipal inspectors, hired on behalf of section 8 housing authorities, with multiple layers of immunity from appeals.

These inspectors terrorize property owners right into arms of dirt-bag contractors, who charge thousands in unnecessary remodel construction. The response of private-property owners behind the Orange curtain (Orange county, CA), is to stop accepting HUD & section 8 vouchers.

Gulf-War veterans are the casualties of this exploit, since their Housing vouchers expire before finding a property. Some private holdouts still taking HUD are already occupied in Orange county. A small public-housing compound remains in Anaheim, but the last private owners opening new Housing vouchers are down to a few retirement communities, exclusively for age 62 & over.

Complaints about Housing inspectors are still raised at our Orange Empire IAEI meetings, where the education chair & senior municipal planner tries to describe all the barriers for appeal, which are never successful.

Jurisdiction is the first barrier to appeal:
Inspection agents hired by State or Federal Housing authorities are not subject to the NEC, nor GFCI's per 406.4(D)(2) replacement code, unless Housing Authorities are specifically included by local or State laws.

Neither is IAEI, their education chair, nor municipal planners legally allowed share copies of any such laws, without being subject to prosecution from private publishers. The critical laws regarding jurisdiction are hidden behind proprietary firewalls, searchable only by appellate attorneys, and those with access to private-legal databases, such as the old Lexis Nexis.

Bureaucracy Delays are another barrier to appeal:
Property owners trying to appeal unnecessary construction, and remodel contractors --imposed by Housing inspectors-- can get their occupancy revoked, waiting months to find out if any AHJ, much less any court is willing to hear the case.

Every one of my clients surrendered to this exploit, after getting screwed by these jerks that carefully avoid specific-contractor recommendation, since a conflict of interest would breach their Vail of immunity. Good luck if you decide to appeal.
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
Our Housing inspectors also fail GFCI's protection of 2-wire cables, demanding grounding wire.

I have run into this with fridges, freezers, ceiling and bathroom fans on older two wire cable, as fans are motors 250.112(C) Applies, 410.44 Exception 3 does not apply to anything other than a 'luminaire' (fixture). If there is an accessible attic I often see a #12 Green fished in to retrofitted fan boxes where old two wire cable is still the supply.
There is no AFCI requirement when replacing fixtures like-for-like.
However 410.21 is a Gotcha for buildings built before 1985 with older 60C type TW and 'NM' cable. There have been many documented fires attributed to overheated wires in lighting boxes. I have never seen any residential wiring rated over 60C in an un-renovated older than 1985 building. Therefore 2 feet of new 90C wiring would need to be run to the fixtures that require 90C wire.
And in this case 210.12(D) Exception would still exempt you from AFCI.
Cheers
 

GerryB

Senior Member
I have run into this with fridges, freezers, ceiling and bathroom fans on older two wire cable, as fans are motors 250.112(C) Applies, 410.44 Exception 3 does not apply to anything other than a 'luminaire' (fixture). If there is an accessible attic I often see a #12 Green fished in to retrofitted fan boxes where old two wire cable is still the supply.
There is no AFCI requirement when replacing fixtures like-for-like.
However 410.21 is a Gotcha for buildings built before 1985 with older 60C type TW and 'NM' cable. There have been many documented fires attributed to overheated wires in lighting boxes. I have never seen any residential wiring rated over 60C in an un-renovated older than 1985 building. Therefore 2 feet of new 90C wiring would need to be run to the fixtures that require 90C wire.
And in this case 210.12(D) Exception would still exempt you from AFCI.
Cheers
What do you mean by run 2 feet of new wire, to where? I may have heard something about this in the past. A new fixture has 90C leads, can you install it on a box that has K&T in it?
 

kwired

Electron manager
Location
NE Nebraska
He would typically be hired by the town manager, or board of selectman. But they cannot overrule his professional decision. We have a procedure to appeal his decision to the State Board of Electrical Examiners. I'm hoping it doesn't come to that.



This was the Town wiring inspector, not an inspector from the Housing Authority. I've run into housing and health regulations/ codes that require more than is required by the NEC.
Sorry you have a one man inspection authority - that is often never good, especially if you get one of those people that think they are never wrong. Also too bad you appear to have a state authority that thinks they are too busy to do their job.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
I have run into this with fridges, freezers, ceiling and bathroom fans on older two wire cable, as fans are motors 250.112(C) Applies, 410.44 Exception 3 does not apply to anything other than a 'luminaire' (fixture)..

Yes, I see. Prior to the 1960's grounding & NEC section 250 is not required, if exiting building wiring is not modified. However most existing structures have been modified.

Adding any window/wall/central HVAC, or attic/ceiling/bath/range-vent fans, or appliances missing extra-hard usage cords, triggers NEC 250.110/.112. Bonded outlets are now required for those appliances, but the existing building does not require a total rewire / remodel.

For the rest of the existing building replacement code NEC 406.4(D)(2) applies, where GFCI's provide superior protection to antiquated grounding systems that remain hazardously energized during low-level faults.

AFCI's should only be required for replacement receptacles 404.4(D)4, and new work over 6ft 210.12, which includes new switch legs >6ft for ceiling fans.
 

JohnE

Senior Member
Location
Milford, MA
My original email to him in red, followed by his reply in blue:

Hi Ted,

I just want to follow up on our phone conversation from Friday, regarding the paddle fan/ lights we installed to replace existing ceiling lights at XXX Rd. I agree that article 210.12A requires Arc-Fault protection for all 120-volt, single-phase, 15-and 20-amp branch circuits supplying outlets or devices installed in dwelling unit kitchens, family rooms, etc. However, my interpretation is that based on the definition of an outlet, (a point on the wiring system at which current is taken to supply utilization equipment) this isn’t a new outlet. It’s a new box and new fan/ fixture. It also is not a new device, as it isn’t a device based on that definition. So I don’t believe that adding AFCI protection is required. I’m hoping you will reconsider your interpretation.

I did post up this question on the Mike Holt Forum. Here is the link:
https://forums.mikeholt.com/showthread.php?t=196109&p=1974396#post1974396

I don’t know if it will get many responses, as it is a topic that has been discussed a few times over the years. This forum has some of the foremost code experts in the country that participate in many discussions. I’ve been on the site for a long time, and I’ve really learned a lot over the years. As I said, these opinions and interpretations carry no more weight than yours or mine, but it’s a good site, with many helpful members.

Sincerely,

John


John,

The work you did was a modification of the branch circuit wiring per Article 210 Branch Circuits 210.12 arc-fault circuit interrupter protection 210.12(D) extensions or modifications. The addition of the paddle fan is an additional outlet that requires arc fault protection. Article 100 Definitions - Outlet. A point on the wiring system at which current is taken to supply utilization equipment. Article 210.12 (A) arc-fault circuit protection would then apply.

If anyone has any additional suggestions on how to convince him that he is misinterpreting this code, it would be appreciated. Otherwise I am still waiting as to whether the customer wants me to appeal his decision, or come up with the money to install AFCI breakers (and any associated troubleshooting/ repairs, if necessary).
 

kwired

Electron manager
Location
NE Nebraska
My original email to him in red, followed by his reply in blue:

Hi Ted,

I just want to follow up on our phone conversation from Friday, regarding the paddle fan/ lights we installed to replace existing ceiling lights at XXX Rd. I agree that article 210.12A requires Arc-Fault protection for all 120-volt, single-phase, 15-and 20-amp branch circuits supplying outlets or devices installed in dwelling unit kitchens, family rooms, etc. However, my interpretation is that based on the definition of an outlet, (a point on the wiring system at which current is taken to supply utilization equipment) this isn’t a new outlet. It’s a new box and new fan/ fixture. It also is not a new device, as it isn’t a device based on that definition. So I don’t believe that adding AFCI protection is required. I’m hoping you will reconsider your interpretation.

I did post up this question on the Mike Holt Forum. Here is the link:
https://forums.mikeholt.com/showthread.php?t=196109&p=1974396#post1974396

I don’t know if it will get many responses, as it is a topic that has been discussed a few times over the years. This forum has some of the foremost code experts in the country that participate in many discussions. I’ve been on the site for a long time, and I’ve really learned a lot over the years. As I said, these opinions and interpretations carry no more weight than yours or mine, but it’s a good site, with many helpful members.

Sincerely,

John


John,

The work you did was a modification of the branch circuit wiring per Article 210 Branch Circuits 210.12 arc-fault circuit interrupter protection 210.12(D) extensions or modifications. The addition of the paddle fan is an additional outlet that requires arc fault protection. Article 100 Definitions - Outlet. A point on the wiring system at which current is taken to supply utilization equipment. Article 210.12 (A) arc-fault circuit protection would then apply.

If anyone has any additional suggestions on how to convince him that he is misinterpreting this code, it would be appreciated. Otherwise I am still waiting as to whether the customer wants me to appeal his decision, or come up with the money to install AFCI breakers (and any associated troubleshooting/ repairs, if necessary).
I think depending on how one interprets things you both can be right. I myself lean more toward a new outlet wasn't created, but can see it being interpreted otherwise by the AFCI extremists.
 