Haven't seen EMT used for any installations since I was doing my apprenticeship in the 1840s....and even then we had to run a separate earth (grounding) conductor...
Haven't seen EMT used for any installations since I was doing my apprenticeship in the 1840s....and even then we had to run a separate earth (grounding) conductor...
Seen many from the time period you mentioned with poorly supported raceway contributing to broken fittings resulting in loss of EGC, also seen loose set screws or compression nuts, but that is all workmanship issues more than anything IMO. Have seen poorly made up EGC's in cable wiring methods as well - open continuity is still open continuity.
I do a lot of grain storage bins and handling equipment. Generally all steel structures and equipment. I do run EGC's in flexible conduits or in any non metallic raceways (which is usually just underground raceways in these applications) but see running any wire EGC in most of said systems as pointless, the equipment/structures are very effective fault return path, and usually more effective than my raceways, so if a fitting didn't get tightened it doesn't really matter much from equipment grounding perspective.
Agree, if set screws are tight then your are good to go, but Ive come across installations [done by others] with duck tape used for couplings.
Agree, if set screws are tight then your are good to go, but Ive come across installations [done by others] with duck tape used for couplings.
And also seen 1/2 FMC fittings used for 3/4 EMT. Works great when you ran 3/4 but didn't know how to enlarge a 1/2 KO, or if you needed a 90 degree connector
It comes down to installation... in UK and USA I don’t run into much rusted out emt, so the use of it for ground is fine. In Caribbean I run into a lot of rusted out emt with no continuity of ground... so in Caribbean I always add a ground conductor...
Student of electrical codes. Please Take others advice first.
It comes down to installation... in UK and USA I don’t run into much rusted out emt, so the use of it for ground is fine. In Caribbean I run into a lot of rusted out emt with no continuity of ground... so in Caribbean I always add a ground conductor...
It seems to me that if the EMT is rusting out it is not suitable to use it at all in that location.