Reason for dedicated space above electrical switchboards

Status
Not open for further replies.
Article 110.26(E) of the NEC states that you need a dedicated equipment space above panels, switchboards or motor control centers that is either 6 feet in height or to a structural ceiling whichever is lower. Why is this space required? Is it for future access to the top of these pieces of equipment? I have an installation that has ductwork only about 8 inches above 2 switchboards which are my normal and emergency service entrance switches. The feeder conduits come out of the bottom and no more feeders will ever come out of either switchboard. Why do I need the clearance on the top?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
You need the clearance because the nec requires it. :D But is it not possible that someday down the road you may need to abandon something and come out the top?

Also if it is duct work is it possible for condensation to drip on the panel. Normally that is not an issue but I have seen it. BTW, you may be able to get a variance- talk with the inspector.

(b) Foreign Systems. The area above the dedicated space
required by 110.26(E)(1)(a) shall be permitted to contain
foreign systems, provided protection is installed to avoid
damage to the electrical equipment from condensation, leaks,
or breaks in such foreign systems.


BTW welcome to the forum
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
My belief, for which I have no supporting evidence, is that the rule exists to enable you to install conduits in the future, without having to deal with interferences from foreign systems. That is why, again as I believe, the rule only applies to switchgear (added recently), switchboards, panelboards, and MCCs. Those are the only components for which the installation of future conduits is likely.

You said you were dealing with the service SWITCHES. Are they just switches, or are they SWITCHBOARDS? If the former, then the rule does not apply to your installation.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
6' is a ridiculous amount of space especially in old existing buildings that are being renovated or upgraded.
 

sameguy

Senior Member
Location
New York
Occupation
Master Elec./JW retired
Why wouldn't you want space?
Our trade is last on everything so the few times we are "granted" space I prefer not to relinquish any.
 