    Residential garage

    The basement/ garage area of a common “A” frame home in my area has a steel beam running thru the center of the home at a 90 degree angle to floor joists. In the basement laundry part bored holes are common rules pretty straight forward.

    But the typical garage has a finished ceiling and the nm cables are attached/ bundled between finished ceiling and steel beam exposed. Is this code compliant?

    After the steel beam ends wires are bundled run along wall finished ceiling height to service panel drop about a foot then enter panel is this OK

    334.15C gives some good info as does 300.4 but I’m having trouble. With the garages here having finished ceilings and the above methods seeming so common and probably incorrect is what causes me confusion

    Thanks for your help

    #2
    Originally posted by dm9289 View Post
    The basement/ garage area of a common “A” frame home in my area has a steel beam running thru the center of the home at a 90 degree angle to floor joists. In the basement laundry part bored holes are common rules pretty straight forward.

    But the typical garage has a finished ceiling and the nm cables are attached/ bundled between finished ceiling and steel beam exposed. Is this code compliant?

    After the steel beam ends wires are bundled run along wall finished ceiling height to service panel drop about a foot then enter panel is this OK

    334.15C gives some good info as does 300.4 but I’m having trouble. With the garages here having finished ceilings and the above methods seeming so common and probably incorrect is what causes me confusion

    Thanks for your help
    I am having a hard time understanding what you are describing in bold print above.

    Steel beam is presumably there to support ceiling framing members as they probably aren't rated to span wall to wall, how is it you have a space between it and the ceiling to bundle the cables?
    I live for today, I'm just a day behind.

    Comment


      #3
      The word "bundled" raises eyebrows...watch 310.15(B)(3) !
      At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

      Comment


        #4
        Typically in this area a wooden beam is on top of steel beam and it is attached between steel wood and ceiling

        Comment


          #5
          Originally posted by dm9289 View Post
          Typically in this area a wooden beam is on top of steel beam and it is attached between steel wood and ceiling
          So you essentially have a wood beam below and supporting the joists, and an additional steel beam below and supporting it? Don't see what is gained by that but not really relevant to your question either. I take it cables in question are attached to this wood beam? If AHJ considers them protected from physical damage then it is probably fine to run them there. Whether or not they are considered bundled or not may require you apply ampacity adjustments.
          I live for today, I'm just a day behind.

          Comment


            #6
            Click image for larger version

Name:	image.jpg
Views:	1
Size:	161.2 KB
ID:	2380383

            Comment


              #7
              Originally posted by dm9289 View Post
              [ATTACH=CONFIG]22251[/ATTACH]
              Your "wood beam" is more of a continuous "shim" than it is a beam. It alone is not adding strength to the beam. But is now clear what you were describing. In that image I'd say that cable is not exposed after finish is put on those vertical strips. Could possibly need protection nail plates if not over 1-1/4 inch from face of strip to the cable though.
              I live for today, I'm just a day behind.

              Comment


                #8
                Originally posted by augie47 View Post
                The word "bundled" raises eyebrows...watch 310.15(B)(3) !

                Yes if you look at the beam picture I posted it would be similar to that with a drywall ceiling. Lets say 8 NM cables typically tie wrapped to create the bundle. I am not sure how to derate no conduit

                Comment


                  #9
                  The picture I posted is an example of the beam but the finished garage ceiling is what is different. Typically you will see 8 NM cables tie wrapped across the beam then 90 degree angle attached in corner of ceiling and block wall then a 90 downward to panel. Hope this clears my description up.

                  Comment


                    #10
                    I honestly don't see how NM ever survives at all.

                    You would think the wiring methods designed for a dwelling type installation would be more robust.

                    Oh well,,,,


                    JAP>

                    Comment


                      #11
                      Originally posted by dm9289 View Post
                      Yes if you look at the beam picture I posted it would be similar to that with a drywall ceiling. Lets say 8 NM cables typically tie wrapped to create the bundle. I am not sure how to derate no conduit
                      Same way you "derate" conductors in a conduit. If you have eight 12-2 cables bundled together you have 16 current carrying conductors and adjustment factor for that is 50%.

                      If you break it into two separate bundles and maintain spacing so that it remains as two separate bundles now you only have 8 current carrying conductors in each bundle and adjustment is 70% - that works out to not needing to increase conductor size for NM-B.

                      Reality is you probably never produce enough heat to be an issue unless they are all feeding HVAC or other continuous loads, but that is not what NEC says....
                      I live for today, I'm just a day behind.

                      Comment


                        #12
                        Originally posted by dm9289 View Post
                        The picture I posted is an example of the beam but the finished garage ceiling is what is different. Typically you will see 8 NM cables tie wrapped across the beam then 90 degree angle attached in corner of ceiling and block wall then a 90 downward to panel. Hope this clears my description up.
                        Nope. Even more confusing. How about a picture?

                        -Hal

                        Comment


                          #13
                          3M cable stackers, but you can bundle w/ tywraps.

                          Comment


                            #14
                            Originally posted by dm9289 View Post
                            The basement/ garage area of a common “A” frame home in my area has a steel beam running thru the center of the home at a 90 degree angle to floor joists. In the basement laundry part bored holes are common rules pretty straight forward.

                            But the typical garage has a finished ceiling and the nm cables are attached/ bundled between finished ceiling and steel beam exposed. Is this code compliant?

                            After the steel beam ends wires are bundled run along wall finished ceiling height to service panel drop about a foot then enter panel is this OK

                            334.15C gives some good info as does 300.4 but I’m having trouble. With the garages here having finished ceilings and the above methods seeming so common and probably incorrect is what causes me confusion

                            Thanks for your help
                            If you are saying they are only bundled for a foot then you are ok. That is the same as a sleeve less than 24" NEC 310.15(B)(3) in 2014, adjustment factors, more than 3 current carrying conductors.