Insight needed

Status
Not open for further replies.

tonype

Senior Member
Location
New Jersey
Saw this in an attic... 2 fuses. The connections at the top go into am ampere meter. Any insight into this would be appreciated.
 

Attachments

  • DSCF7066.jpg
    DSCF7066.jpg
    149.8 KB · Views: 0
  • DSCF7065.jpg
    DSCF7065.jpg
    143.9 KB · Views: 0

david

Senior Member
Location
Pennsylvania
Not very consistent with the colors they used for the ungrounded and grounded conductors

The inline fuse for the duplex receptacle mounted above the amp meter

The amp meter in in series with the ungrounded conductor top left BX cable, feeding something not in the picture
 

hbiss

EC, Westchester, New York NEC: 2014
Location
Hawthorne, New York NEC: 2014
Occupation
EC
No, it appears that the receptacle is and is fed through the fuse holder and that purple jumper. The cables, one going down and the other off to the right are loads also.

-Hal
 

__dan

Senior Member
Saw this in an attic... 2 fuses. The connections at the top go into am ampere meter. Any insight into this would be appreciated.

It is very homemade and non standard. Most likely it is something that the homeowner should be advised, take it out. After disconnecting it, if you find it fed something that you still need, you can consider repowering the load.

The meter belongs in a curio collection. The installation was not done by a regular trade contractor. It's a unicorn.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
To either reiterate or add to the above, in no particular order:

It's a 120v "service" with an ammeter, not a watt-hour meter.

Could be a "sub-panel" not the service; check other side of wall.

Feed coming in from upper-left cable coming through the wall.

The conductor coloring is not consistent throughout installation.

Top of the enclosure was butchered to accommodate ammeter.

Both ungrounded and grounded conductors switched and fused.

Receptacle above is also used through fuse-holder on bottom.

Service rating appears to be stuck through on label on door.

It's probably better and safer than some wiring I have seen.
 

kwired

Electron manager
Location
NE Nebraska
Agree with larry, likely is 120 volt supply, from the top left cable. Look carefully the black conductor goes to top left terminal of disconnect. White disappears on us but pretty sure is the one landing on left ammeter lead, then right ammeter lead lands on the top right terminal of disconnect. Lots of old installations had fuse in both lines, some may not even been grounded originally and maybe part of reason why fuse in both lines. They are metering the white supply lead (whether it is grounded or not).
 