    Insight needed

    Saw this in an attic... 2 fuses. The connections at the top go into am ampere meter. Any insight into this would be appreciated.
    Attached Files
    Tony Shupenko, PE

    #2
    what is/was it feeding?

    Comment


      #3
      Originally posted by rambojoe View Post
      what is/was it feeding?
      Don't know... likely lighting and receptacles.
      Tony Shupenko, PE

      Comment


        #4
        Not very consistent with the colors they used for the ungrounded and grounded conductors

        The inline fuse for the duplex receptacle mounted above the amp meter

        The amp meter in in series with the ungrounded conductor top left BX cable, feeding something not in the picture

        Comment


          #5
          Originally posted by tonype View Post
          Don't know... likely lighting and receptacles.
          my first thought was some type of motor repair station but the rec above the amp meter is not tied to the amp meter

          have no idea

          Comment


            #6
            No, it appears that the receptacle is and is fed through the fuse holder and that purple jumper. The cables, one going down and the other off to the right are loads also.

            -Hal

            Comment


              #7
              Originally posted by tonype View Post
              Saw this in an attic... 2 fuses. The connections at the top go into am ampere meter. Any insight into this would be appreciated.
              It is very homemade and non standard. Most likely it is something that the homeowner should be advised, take it out. After disconnecting it, if you find it fed something that you still need, you can consider repowering the load.

              The meter belongs in a curio collection. The installation was not done by a regular trade contractor. It's a unicorn.
              Lasciate ogne speranza, voi ch'intrate

              Comment


                #8
                To either reiterate or add to the above, in no particular order:

                It's a 120v "service" with an ammeter, not a watt-hour meter.

                Could be a "sub-panel" not the service; check other side of wall.

                Feed coming in from upper-left cable coming through the wall.

                The conductor coloring is not consistent throughout installation.

                Top of the enclosure was butchered to accommodate ammeter.

                Both ungrounded and grounded conductors switched and fused.

                Receptacle above is also used through fuse-holder on bottom.

                Service rating appears to be stuck through on label on door.

                It's probably better and safer than some wiring I have seen.
                Master Electrician
                Electrical Contractor
                Richmond, VA

                Comment


                  #9
                  Never thought of a service in an attic space, could be though its old enough

                  Comment


                    #10
                    Agree with larry, likely is 120 volt supply, from the top left cable. Look carefully the black conductor goes to top left terminal of disconnect. White disappears on us but pretty sure is the one landing on left ammeter lead, then right ammeter lead lands on the top right terminal of disconnect. Lots of old installations had fuse in both lines, some may not even been grounded originally and maybe part of reason why fuse in both lines. They are metering the white supply lead (whether it is grounded or not).