  • c_picard
    replied
    Thanks. I don't think I could make a decent case against your Class 1 argument.

    Overcurrent protection is another item that points to 450.

    725.45(D) > 450.3(B) > Table 450.3(B) = 125% of primary current?

    But 450.1 Exception No. 1 excludes CTs altogether.

    I think the Code might be broken, hand me a sledgehammer.

    Leave a comment:


  • petersonra
    replied
    I think one can make a good argument that CTs circuits are indeed class 1 circuits.

    Having said that, there does not seem to be an exception for the required OCPD in the transformer circuit found in article 725.

    Leave a comment:


  • c_picard
    started a topic Current Transformer (CT) Secondary Wiring

    Current Transformer (CT) Secondary Wiring

    Does the CT secondary wiring need to be rated 600V for installation in a 120/240V panel?

    Is this considered Class 1 wiring subject to Article 725? Or does 300.3(C) cover this sufficiently?

    I ask because 725 point to 450, but CTs are explicitly excluded from the scope.