    outlet in sheetrock encapsulated column

    hello

    will someone please tell me whether or not its code compliant to install an outlet in a sheetrock column which is encapsulating a steel column? its in a church sanctuary thanks the sheetrock is three layers thick thank you for the great help
    Ravenvalor
    Electrical Contractor
    Piedmont Region of NC

    "Good day and good premises." (Ayn Rand)

    #2
    you would have to maintain the fire rating of the assembly

    https://www.nationalgypsum.com/file/...ok_May2014.pdf

    Page 86 3 hr fire rating

    Comment


      #3
      I've done it but the columns were spray coated before and the print showed them going there; so stamped by engineers. Three layers of rock sounds like fire protection, look at fire barrier wraps. Not sure what 3 layers of 5/8 or 1/2, or 1" gives in hours.

      Comment


        #4
        Fixed Poster

        Since it's surround a column and there are 3 layers than as David stated you'll need to be conscious of the fire rating of the column. Metal boxes generally have a 2 hour fire rating.
        Last edited by infinity; 02-12-19, 05:43 PM.
        Rob

        Moderator

        All responses based on the 2017 NEC unless otherwise noted

        Comment


          #5
          Wow.... Thanks for all of the great replies. Babe Ruth would be proud of you all for knocking this one out of the park for me...