outlet in sheetrock encapsulated column

Status
Not open for further replies.

Ravenvalor

Senior Member
hello

will someone please tell me whether or not its code compliant to install an outlet in a sheetrock column which is encapsulating a steel column? its in a church sanctuary thanks the sheetrock is three layers thick thank you for the great help
 

sameguy

Senior Member
Location
New York
Occupation
Master Elec./JW retired
I've done it but the columns were spray coated before and the print showed them going there; so stamped by engineers. Three layers of rock sounds like fire protection, look at fire barrier wraps. Not sure what 3 layers of 5/8 or 1/2, or 1" gives in hours.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Fixed Poster

Fixed Poster

Since it's surround a column and there are 3 layers than as David stated you'll need to be conscious of the fire rating of the column. Metal boxes generally have a 2 hour fire rating.
 
Last edited: