    Cord Connected Fixtures

    Just curious as to how often you find violations of 410.62(C) ?
    On a huge percentage of the installs (especially convenience stores) in this area the fixture cords are hard wired with cord to the box or the cord is run behind insulation or tied to the building structure.

    All I ever hear is "I do it all the time, everywhere" !!
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

    #2
    Originally posted by augie47 View Post
    Just curious as to how often you find violations of 410.62(C) ?
    On a huge percentage of the installs (especially convenience stores) in this area the fixture cords are hard wired with cord to the box or the cord is run behind insulation or tied to the building structure.

    All I ever hear is "I do it all the time, everywhere" !!
    Learned this through an EC friend back under the 2014 cycle. He had a job for a local city rec center...one-for-one replacement of EXISTING fixtures, all served via a cord from an outlet box above.
    Awarded the job, replaced the fixtures and local EI rejected stating this code section.

    He changed all and added cord & plug on his dime....I tried to get him to argue with the state board of appeals. Local code, as I understand it is...unless a imminent safety hazard, existing conditions are what they are.

    I ran it past lighting reps and factories, and they seemed oblivious to the wording.
    It appears they have edited for 2017.

    Comment


      #3
      Originally posted by augie47 View Post
      Just curious as to how often you find violations of 410.62(C) ?
      On a huge percentage of the installs (especially convenience stores) in this area the fixture cords are hard wired with cord to the box or the cord is run behind insulation or tied to the building structure.

      All I ever hear is "I do it all the time, everywhere" !!
      I do disagree with the install if the cord is not visible for it's entire length, however, I question why the rule would allow a cord to be terminated to a busway plug (which to me would simply be a cord connector into a knockout) yet it seems to not allow the cord to terminate the same way into a standard 4 square box.

      What's up with that?

      JAP>

      Comment


        #4
        If you are going to connect directly to a box, why not just do it right with an AC/MC/Greenfield whip?

        -Hal

        Comment


          #5
          Originally posted by hbiss View Post
          If you are going to connect directly to a box, why not just do it right with an AC/MC/Greenfield whip?

          -Hal
          Cords are allowed, but, how does adding a male cord cap to a cord, and, plugging it into a receptacle above the fixture, make it any more right than to hard wire the cord directly to the fixture ?

          JAP>

          Comment


            #6
            Originally posted by hbiss View Post
            If you are going to connect directly to a box, why not just do it right with an AC/MC/Greenfield whip?

            -Hal
            MC or any other wiring method with solid conductors would not be permitted.

            Comment


              #7
              Originally posted by norcal View Post
              MC or any other wiring method with solid conductors would not be permitted.
              Per what code section?

              There are pre-assembled FMC fixture whips with solid conductors in them, usually 16 or 18 AWG but still is solid.
              I live for today, I'm just a day behind.

              Comment


                #8
                Originally posted by kwired View Post
                Per what code section?

                There are pre-assembled FMC fixture whips with solid conductors in them, usually 16 or 18 AWG but still is solid.
                410.55(E) but only applies to chains or other flexible mounted fixtures.

                Comment


                  #9
                  Originally posted by norcal View Post
                  410.55(E) but only applies to chains or other flexible mounted fixtures.
                  Stranded conductors shall be used for wiring on luminaire chains and on other movable or flexible parts.
                  Is wiring method supplying the luminaire part of the luminaire or part of premises wiring? My thought is part of premises wiring. I also think ever since they stated luminaires must be listed, some of the rules such as this one are no longer needed, it is design requirements for something that should already be covered in the listing.
                  I live for today, I'm just a day behind.

                  Comment