Residential Service Location
HoosierSparky
Senior Plans Examiner, MEP
Scottsdale AZ
I have a homeowner that does not want to pay for the utility to bring service wiring under an alley, through the yard and to the front side of their home. The utility is selecting the meter location. They have proposed setting a pole in the back corner of the yard and placing the electrical service equipment on the pole. From there, trench underground to the current service location and set a sub-panel to service the existing wiring. The building official is calling the pole a structure, so that would satisfy the code requirement of service equipment being mounted to a structure.
I cannot find any CODE that would prevent this type of installation. Thoughts?
View attachment Proposed Res Service.pdf
augie47
Tennessee
I know of no problem. Locally you would not need anything (meter or disconnect) on the pole itself as it simply relocates your "service point" but your local AHJ or POCO might require either or both at the pole.
HoosierSparky
Scottsdale AZ
The POCO wants the meter relocated IF they are providing new service lines.
david
Pennsylvania
Be careful there is a difference between installing a meter on a utility pole verses installing service equipment on a utility pole.
Here if the utility owns the pole it would be unlikely they would allow anything other than a meter installed on there pole
The utility would allow other utilities to utilize there pole (cable, phone)
Make sure you have power company permission.
Also take into consideration cable or phone utilities in your planning
Personally i would rather just install the meter on the pole and leave the service location where it is
HoosierSparky
Scottsdale AZ
Thanks! Elegant solution. It will look a lot better on the site, too. I will make the suggestion to them. Thanks!!