PVC Male Adapter

Status
Not open for further replies.

jap

Senior Member
Occupation
Electrician
It is if a nicked conductor should make contact with the EMT.

Edit: I think you just like to argue, :lol:

No.

An EMT connection to the box at the top would make no difference whatsoever.

In a branch circuit from the source, If there's a nicked conductor in the EMT Stub up between the PVC stubup at the floor and the top of the stub out where it's connected to the metal box, a connector connection is not going to clear that fault whatsoever.

Only a wire type EGC pulled in the raceway and bonded to the metal box would would.

If the EMT inside the block was terminated to a surface mount PVC box a the top where it stubs out, without and wire type EGC pulled in the conduit, there would be no fault clearing capability at all.

The only way you'd get shocked would be if you took the cover off of the PVC box at the top and put yourself between the energized metal connector in the back of the box, or, was silly enough to knock a hole in the block wall and grab ahold of the energized EMT stub up and something that was actually grounded.


JAP>
 

Adamjamma

Senior Member
In Jamaica the standard seems to be asyou described, stubbing the pvc into the box without an adapter, then capping the pvc with paper as you pour the concrete..l prefer to use adaptors but often have customers complain about the cost of them. Inspectors are pretty much non existent except for initial meter installs here soelectricians pretty much n their own
 