Handle Ties

Status
Not open for further replies.

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
City of Glendale (California) is now requiring Handle Ties on twin breakers that fit in a standard breaker space. This is not a "Multi Wire" circuit ? But if that's what they want a bag of ten is only $4.95.
 

jap

Senior Member
Occupation
Electrician
Maybe because when your dealing with the load end of a piggy back breaker they want both load terminals that are in close proximity de-energized ?

Not sure.



JAP>
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
That's weird for two reasons:

1. Same phase so there's no shared neutral.

2. I've never seen a handle tie that small.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
Why do they want handle ties on CB's that are not supplying a MWBC?

My best guesses....
1.) Ignorant person making the local amendments
2.) They know that "Hammering Handy Hank" thinks he is making a MWBC with the twin breakers and they want both breakers off if working on it. But that doesn't address overloading the neutral!;)
 

MAC702

Senior Member
Location
Clark County, NV
Why don't we just require main breakers to be shut off (and from a separate main disconnect) before any electrical work is done? If it saves just one idiot... :rant:
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
(1) How would you install a handle tie on a twin breaker? All that I can think of require the handles to be spread apart to install.

(2) Unless they have filed a formal amendment with the State of California they can't require it. They must follow the CEC.
 

kwired

Electron manager
Location
NE Nebraska
That's weird for two reasons:

1. Same phase so there's no shared neutral.

2. I've never seen a handle tie that small.

My thought immediately - there is no handle ties other than the "homemade" type that would fit them. I know a QO handle tie will work between adjacent tandem breakers to make a MWBC out of the inner two handles, but they don't make any that fit between two handles on same tandem breaker.

My best guesses....
1.) Ignorant person making the local amendments
2.) They know that "Hammering Handy Hank" thinks he is making a MWBC with the twin breakers and they want both breakers off if working on it. But that doesn't address overloading the neutral!;)

Bingo. May not be allowed to make such amendments by law from what it sounds like either.
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
My best guesses....
1.) Ignorant person making the local amendments
2.) They know that "Hammering Handy Hank" thinks he is making a MWBC with the twin breakers and they want both breakers off if working on it. But that doesn't address overloading the neutral!;)

(1) How would you install a handle tie on a twin breaker? All that I can think of require the handles to be spread apart to install.

(2) Unless they have filed a formal amendment with the State of California they can't require it. They must follow the CEC.


I bet if you or I were to waste our time and search the filed local amendments we would find nothing.
This a just another wanabe prick inspector touting something he thought he learned. Just another idiot.
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
Updated information, see attachment. View attachment Siemens Handle Ties, 03-30-2019.pdf

I was wrong ! ... The handle ties are for the multi-wire circuits. The tandem breakers on a residential panel are in either H1 or H2. But when two or more tandem breakers are used you will have a multi-wire circuit. After installing the attached handle ties it passed inspection.
 

Sierrasparky

Senior Member
Location
USA
Occupation
Electrician ,contractor
Updated information, see attachment. View attachment 22710

I was wrong ! ... The handle ties are for the multi-wire circuits. The tandem breakers on a residential panel are in either H1 or H2. But when two or more tandem breakers are used you will have a multi-wire circuit. After installing the attached handle ties it passed inspection.

Hummm, I still don't get what you are speaking of.

If there is no shared neutral there is no MWBC, ( Multi wire BRANCH circuit. ) which may not be what you refer to as a multi wire circuit.


IF there is no neutral then it ain't a MWBC and NO handle ties. It does not matter how many twin breakers used if there is no shared neutral , NO Handle tie. , I don't know what crack your inspector is smoking.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Updated information, see attachment. View attachment 22710

I was wrong ! ... The handle ties are for the multi-wire circuits. The tandem breakers on a residential panel are in either H1 or H2. But when two or more tandem breakers are used you will have a multi-wire circuit. After installing the attached handle ties it passed inspection.

I'm confused here. Those handle ties are for when you have a MWBC connected to 2 adjoining twin breakers. But in your OP I understood you to say you did not have a MWBC in which case you do not need handle ties.
 

mtnelect

HVAC & Electrical Contractor
Location
Southern California
Occupation
Contractor, C10 & C20 - Semi Retired
Handle Ties - Multi Circuits

Handle Ties - Multi Circuits

Correction Notice ...

We normally do commercial installations ... We were caught off guard with this residential service change. A multi circuit that share a neutral now needs a "Handle Tie".
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
Correction Notice ...

We normally do commercial installations ... We were caught off guard with this residential service change. A multi circuit that share a neutral now needs a "Handle Tie".

Now you are changing your story. If you have 2 circuits that share a neutral that is a multi-wire circuit and does require a handle tie or multi pole breaker. Residential and commercial are the same requirements. You can not connect both circuits to the same tandem breaker. They need to be on adjacent breakers which you can use the handle tie you linked to.
 

kwired

Electron manager
Location
NE Nebraska
Correction Notice ...

We normally do commercial installations ... We were caught off guard with this residential service change. A multi circuit that share a neutral now needs a "Handle Tie".
That rule applies everywhere not just residential since either 2008 or 2011 code.

But if both ungrounded conductors are on the same "tandem" you don't have a proper MWBC, the shared neutral in that case is not carrying unbalance current instead current is additive on the neutral. You can have a MWBC between two handles on different tandems on adjacent slots in the panel with a handle tie between the two handles though.
 
Status