The new wording in 210.8 NEC 2018 states that when determining distance for GFCI's it is "would follow without ... passing through a door. My first thought is that if the receptacle has to pass through a door, then a GFCI isn't required on the other side of the door. But I think I have read here where it is believed to be required. Can we discuss the reasoning? I can see where one might state, a cabinet door isn't a "door" in this case, for example.
Announcement
Collapse
No announcement yet.
GFCI Receptacle for garbage disposal
Collapse
X
-
Originally posted by Strathead View PostThe new wording in 210.8 NEC 2018 states that when determining distance for GFCI's it is "would follow without ... passing through a door. My first thought is that if the receptacle has to pass through a door, then a GFCI isn't required on the other side of the door. But I think I have read here where it is believed to be required. Can we discuss the reasoning? I can see where one might state, a cabinet door isn't a "door" in this case, for example.
JAP>
-
I don't see how that can be clearer. IMO, the receptacle under the sink does not need to be gfci protected assuming this is a dwelling.
For the purposes of this section, when determining distance
from receptacles the distance shall be measured as the shortest
path the cord of an appliance connected to the receptacle
would follow without piercing a floor, wall, ceiling, or fixed
barrier, or passing through a door, doorway, or window.
Kitchens — where the receptacles are installed to serve
the countertop surfaces
(7) Sinks — where receptacles are installed within 1.8 m
(6 ft) from the top inside edge of the bowl of the sinkThey say I shot a man named Gray and took his wife to Italy
She inherited a million bucks and when she died it came to me
I can't help it if I'm lucky
Comment
-
Originally posted by Dennis Alwon View PostI don't see how that can be clearer. IMO, the receptacle under the sink does not need to be gfci protected assuming this is a dwelling.
I agree. I would also guess that the specific wording in the NEC that mentions the word door is actually referencing a cabinet door.Rob
Moderator
All responses based on the 2017 NEC unless otherwise noted
Comment
-
Originally posted by LarryFine View PostAjar. At least in my house, it is.
I let my wife do that while I stand guard next to the non-gfi garbage disposal receptacle, just in case some sneaky B_ _ T _ _ D tries to plug something in when we aren't looking.
JAP>
Comment
-
Thank you all I read an old thread where there was much more controversy about it. That wording is not in the 2014 code book. We are still under that one. Do you think an inspector would be wrong to fail you under that code? I think they would be within their rights.
I know what I don't know, and I know where to go to find it!
Comment
-
Originally posted by Strathead View PostThank you all I read an old thread where there was much more controversy about it. That wording is not in the 2014 code book. We are still under that one. Do you think an inspector would be wrong to fail you under that code? I think they would be within their rights.I live for today, I'm just a day behind.
Comment
-
The intent of the 2017 language was that a cabinet door is not a door, but that is not what the words say. The 2020 will remove the words door and doorway from that section to make it clear that receptacles under the cabinet that are within 6' from the sink will require GFCI protection. This change will also require GFCI protection in some unusual locations. For example in my master bedroom the master bath sink is located such that one of the bedroom wall receptacles would require GFCI protection if the 2020 language was applied.Don, Illinois
(All code citations are 2017 unless otherwise noted)
Comment
-
Originally posted by don_resqcapt19 View PostThe intent of the 2017 language was that a cabinet door is not a door, but that is not what the words say. The 2020 will remove the words door and doorway from that section to make it clear that receptacles under the cabinet that are within 6' from the sink will require GFCI protection. This change will also require GFCI protection in some unusual locations. For example in my master bedroom the master bath sink is located such that one of the bedroom wall receptacles would require GFCI protection if the 2020 language was applied.I live for today, I'm just a day behind.
Comment
-
Originally posted by don_resqcapt19 View PostThe intent of the 2017 language was that a cabinet door is not a door, but that is not what the words say. The 2020 will remove the words door and doorway from that section to make it clear that receptacles under the cabinet that are within 6' from the sink will require GFCI protection. This change will also require GFCI protection in some unusual locations. For example in my master bedroom the master bath sink is located such that one of the bedroom wall receptacles would require GFCI protection if the 2020 language was applied.
Electricians disagreeing on whether a cabinet door is not actually a door, pulling 6' strings from the receptacle to the sink for measurements trying to decide whether or not a GFI is required, then disagreeing on exactly how that measurement should be taken.
It's almost comical.
I'm glad our fathers and forefathers didn't waste this much time on such small matters because nothing would have ever gotten accomplished.
Someone make a rule that works and lets roll with it.
This is not that difficult.
JAP>
Comment
-
Originally posted by jap View PostElectricians disagreeing on whether a cabinet door is not actually a door, pulling 6' strings from the receptacle to the sink for measurements trying to decide whether or not a GFI is required, then disagreeing on exactly how that measurement should be taken.
It's almost comical.
I'm glad our fathers and forefathers didn't waste this much time on such small matters because nothing would have ever gotten accomplished.
Someone make a rule that works and lets roll with it.
This is not that difficult.
JAP>
I know what I don't know, and I know where to go to find it!
Comment
-
Originally posted by don_resqcapt19 View Post...The 2020 will remove the words door and doorway from that section to make it clear that receptacles under the cabinet that are within 6' from the sink will require GFCI protection..
See first paragraph of 210.8 and 210.12Roger Ramjet NoFixNoPay
Comment