hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have fire pump 4 pole ats controller breaker all in one at opposite side of main electrical room fed from normal side utility service and emergency side fed from generator which is separetley derived has ground rods as electrode.
Generator is about 40 feet from the main electrical room where their is building ground electrode system.
The fire pump Ats controller breaker all in one needs to be grounded with common ground electrode and has main bonding jumper.
How would this work with the generator side if 4 pole Ats controller breaker fire pump has ground normal side with main bonding jumper?
Generator is about 40 feet from the main electrical room where their is building ground electrode system.
The fire pump Ats controller breaker all in one needs to be grounded with common ground electrode and has main bonding jumper.
How would this work with the generator side if 4 pole Ats controller breaker fire pump has ground normal side with main bonding jumper?