Copper wire size for 200 amp disconnect outside and the main panel inside

Status
Not open for further replies.

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Is 2/0 with 1/0 neutral and #4 ground legal?


We need more info. As asked- dwelling? The grounding electrode conductor will need to be #4 but the equipment grounding conductor from the disconnect outside to the panel inside would only need to be #6
 