S Sttail59 New member Location Morgantown WV USA May 6, 2019 #1 Is 2/0 with 1/0 neutral and #4 ground legal?
Little Bill Moderator Staff member Location Tennessee NEC:2017 Occupation Semi-Retired Electrician May 6, 2019 #2 Sttail59 said: Is 2/0 with 1/0 neutral and #4 ground legal? Click to expand... Is this for a dwelling? Welcome to the forum!
Sttail59 said: Is 2/0 with 1/0 neutral and #4 ground legal? Click to expand... Is this for a dwelling? Welcome to the forum!
LarryFine Master Electrician Electric Contractor Richmond VA Location Henrico County, VA Occupation Electrical Contractor May 7, 2019 #3 Welcome! Might need 3-0. What's your load calc?
Dennis Alwon Moderator Staff member Location Chapel Hill, NC Occupation Retired Electrical Contractor May 7, 2019 #4 Sttail59 said: Is 2/0 with 1/0 neutral and #4 ground legal? Click to expand... We need more info. As asked- dwelling? The grounding electrode conductor will need to be #4 but the equipment grounding conductor from the disconnect outside to the panel inside would only need to be #6
Sttail59 said: Is 2/0 with 1/0 neutral and #4 ground legal? Click to expand... We need more info. As asked- dwelling? The grounding electrode conductor will need to be #4 but the equipment grounding conductor from the disconnect outside to the panel inside would only need to be #6