PVC in a pump room

Status
Not open for further replies.

Alejandro

Member
Location
Orlando, FL
No, I've always seen Ridgid, that's why I asked. I couldn't find anything that says otherwise.
It's odd to me that they would quote a job with Ridgid when you can run PVC

Sent from my SM-N960U using Tapatalk
 

oldsparky52

Senior Member
No, I've always seen Ridgid, that's why I asked. I couldn't find anything that says otherwise.
It's odd to me that they would quote a job with Ridgid when you can run PVC

Sent from my SM-N960U using Tapatalk

Have you checked the PoCo requirements? They would have a say on this since it's their side of the meter.

Is it their side of the meter? I assumed so when you said "Service wire coming underground" in the OP.
 

gadfly56

Senior Member
Location
New Jersey
Occupation
Professional Engineer, Fire & Life Safety
Have you checked the PoCo requirements? They would have a say on this since it's their side of the meter.

Is it their side of the meter? I assumed so when you said "Service wire coming underground" in the OP.

Probably not. Fire pump conductors are treated as service conductors no matter what.
 