    neutral of a branch circuit be reduced in size

    We have a 54 KW boiler, 240 single phase that is continuous duty which is 281 amps. Will feed with (2) 300 KCMILL conductors on 300 amp OCPD. There is a small neutral load of less than 3 amps. Can the neutral of a branch circuit be reduced in size from the phase conductors. If so where is it in the NEC?

    #2
    Is there an OCP device at the furnace making this circuit a feeder or is it actually the branch circuit to the furnace ?
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

    Comment


      #3
      If is is a feeder then yes but the neutral cannot be smaller than the required equipment grounding conductor. If it is a branch circuit then IMO, you cannot. So run a feeder to the equipment and use a disconnect with overcurrent protective device and then you are good to go
      They say I shot a man named Gray and took his wife to Italy
      She inherited a million bucks and when she died it came to me
      I can't help it if I'm lucky

      Comment


        #4
        Originally posted by Dennis Alwon View Post
        If is is a feeder then yes but the neutral cannot be smaller than the required equipment grounding conductor. If it is a branch circuit then IMO, you cannot. So run a feeder to the equipment and use a disconnect with overcurrent protective device and then you are good to go
        What says that the grounded and ungrounded conductors for a branch circuit must be the same size?
        Don, Illinois
        (All code citations are 2017 unless otherwise noted)

        Comment


          #5
          Originally posted by don_resqcapt19 View Post
          What says that the grounded and ungrounded conductors for a branch circuit must be the same size?
          Interesting..
          I was heading the same direction as Dennis (I think) in that Feeders (and services) give the allowance for neutral reduction but I fond no such wording in Art 210.
          It appears in the OPs situation, 210.19 would allow a #14.
          At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

          Comment


            #6
            The problem with a reduced neutral in a two wire branch circuit is 240.4, particularly 240.4(D), the smallest conductor in the circuit will govern the size of the circuit and the OCPD.

            Roger