  • mortimer
    replied
    Thanks Dennis

    Leave a comment:


  • Dennis Alwon
    replied
    What is the voltage??

    680.23(B)(3) Equipment Grounding Provisions for Cords. Other than
    listed low-voltages lighting systems not requiring grounding
    wet-niche luminaires that are supplied by a flexible cord or
    cable shall have all exposed non–current-carrying metal parts
    grounded by an insulated copper equipment grounding
    conductor that is an integral part of the cord or cable. This
    grounding conductor shall be connected to a grounding terminal
    in the supply junction box, transformer enclosure, or other
    enclosure. The grounding conductor shall not be smaller than
    the supply conductors and not smaller than 16 AWG.

    Leave a comment:


  • mortimer
    started a topic pool lighting

    pool lighting

    is led pool lighting required to be bonded and grounded?