Swing Plug for Buss

Status
Not open for further replies.

MTW

Senior Member
Location
SE Michigan
Swing Jack Bulldog Bus Plug

Swing Jack Bulldog Bus Plug

Swing jack, bus plugs are not compliant for new installs, because they are not capable of being operated from the floor. An older plant that still has these types, can continue to use them, on their old circuits.
s-l1600.jpg


368.17 (C) Feeder or Branch Circuits. Where a busway is used as a feeder, devices or plug-in connections for tapping off feeder or branch circuits from the busway shall contain the overcurrent devices required for the protection of the feeder or branch circuits. The plug-in device shall consist of an externally operable circuit breaker or an externally operable fusible switch. Where such devices are mounted out of reach and contain disconnecting means, suitable means such as ropes, chains, or sticks shall be provided for operating the disconnecting means from the floor.
 