Short Radius Elbow

Status
Not open for further replies.

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
Question: Okay to use a Jake El inside a wall. (Short Radius Elbow) View attachment 22964

348.42 does not permit it for flexible metal conduit in a covered wall.
350.42 does not permit it for liquidtight flexible metal conduit in a covered wall.
So i'd say no. I don't have time to look for all possible applications.
 

oldsparky52

Senior Member
348.42 does not permit it for flexible metal conduit in a covered wall.
350.42 does not permit it for liquidtight flexible metal conduit in a covered wall.
So i'd say no. I don't have time to look for all possible applications.

I would never install one of those concealed, but ... I'm not sure those code sections would not allow it. If we look at the 358.42 section (EMT), it does not disallow it.
 

K8MHZ

Senior Member
Location
Michigan. It's a beautiful peninsula, I've looked
Occupation
Electrician
Is the 'short radius elbow' listed? If not, it can't be used at all, correct?

Edit to add: I see it is listed. So it could be used anywhere a straight coupling could be used, apparently. For EMT, flexible type conduit apparently, but it's not listed for that anyway.
 
Last edited:
Status
Not open for further replies.
Top