  • curt swartz
    replied
    I still have no idea what the OP is calling a microwave. They stated its not an oven and its not a hood.

    Leave a comment:


  • Sierrasparky
    replied
    Originally posted by infinity View Post
    Range hood/micro combo are typically cord and plug connected and therefore require an individual branch circuit.
    Yes , several code sections point to the same requirement.
    Individual branch circuit.

    OP has not been back, I bet he gets it.

    Leave a comment:


  • infinity
    replied
    Range hood/micro combo are typically cord and plug connected and therefore require an individual branch circuit.

    (4) Range Hoods. Range hoods shall be permitted to be
    cord-and-plug-connected with a flexible cord identified as
    suitable for use on range hoods in the installation instruc-
    tions of the appliance manufacturer, where all of the fol-
    lowing conditions are met:
    (1) The flexible cord is terminated with a grounding-type
    attachment plug.
    Exception: A listed range hood distinctly marked to iden-
    tify it as protected by a system of double insulation, or its
    equivalent, shall not be required to be terminated with a
    grounding-type attachment plug.
    (2) The length of the cord is not less than 450 mm (18 in.)
    and not over 900 mm (36 in.).
    (3) Receptacles are located to avoid physical damage to the
    flexible cord.
    (4) The receptacle is accessible.
    (5) The receptacle is supplied by an individual branch
    circuit.

    Leave a comment:


  • Sierrasparky
    replied
    Originally posted by hbiss View Post
    OP has no idea what he is talking about.

    -Hal
    Easy now.

    Leave a comment:


  • hbiss
    replied
    OP has no idea what he is talking about.

    -Hal

    Leave a comment:


  • Sierrasparky
    replied
    Need to have some type of hood over a range. If gas it needs to exhausted to the outside. Not a NEC thing but a Building code thing.
    Why would one install a range and no hood or downdraft

    Again if it is built in it needs a dedicated circuit. If on a shelf free standing then no.

    Leave a comment:


  • MAC702
    replied
    Originally posted by hbiss View Post
    If it's going over a stove then it HAS to have an exhaust hood!!
    I suppose it's possible that the range has a downdraft. Would that suffice?

    Leave a comment:


  • hbiss
    replied
    Originally posted by hhsting View Post
    Dont follow microwave has no hood. How can hood article apply to microwave?
    If it's going over a stove then it HAS to have an exhaust hood!!

    -Hal

    Leave a comment:


  • Sierrasparky
    replied
    The issue really is the what the manufacture says and also if its rated over 50% of the branch circuit. How many code sections does one need to say " separate or dedicated circuit "

    There is no way around it unless its a free standing unit.

    Leave a comment:


  • electrofelon
    replied
    Originally posted by hhsting View Post
    Dont follow microwave has no hood. How can hood article apply to microwave?

    Sent from my SM-G935U using Tapatalk
    Over the range microwaves usually are a hood unit as well, don't recall ever seeing one that wasn't. I guess you could have a regular micro on a shelf above the range, above a standalone hood or no hood at all.....

    Leave a comment:


  • hhsting
    replied
    Originally posted by Little Bill View Post
    If it's going over the stove/range then it needs a separate circuit. The code says for "hood" and since the MW is there it needs it. Also the MW has an exhaust fan built in.
    Dont follow microwave has no hood. How can hood article apply to microwave?

    Sent from my SM-G935U using Tapatalk

    Leave a comment:


  • Little Bill
    replied
    If it's going over the stove/range then it needs a separate circuit. The code says for "hood" and since the MW is there it needs it. Also the MW has an exhaust fan built in.

    Leave a comment:


  • Sierrasparky
    replied
    You need also follow the mfg instructions. Most I have seen require a separate circuit.
    A 1000w Micro has a input of about 1500w

    Look at 220.23
    Last edited by Sierrasparky; 05-22-19, 07:46 PM. Reason: added article

    Leave a comment:


  • hhsting
    replied
    Originally posted by peter d View Post
    Are you talking over the range or one sitting on the counter? It does not require a separate circuit if the microwave is fixed in place and isn't more than 50% of the branch circuit rating of 20 amps. Practically this means a microwave needs a separate circuit.
    Over the range like in dewelling unit kitchen. Where in code it says all that?
    Last edited by hhsting; 05-22-19, 07:02 PM.

    Leave a comment:


  • peter d
    replied
    Are you talking over the range or one sitting on the counter? It does not require a separate circuit if the microwave is fixed in place and isn't more than 50% of the branch circuit rating of 20 amps. Practically this means a microwave needs a separate circuit.

    Leave a comment: